Why Not Romex In Conduit? - Electrical - DIY Chatroom Home Improvement Forum
Old 11-07-2008, 08:42 PM   #1
DIY Hack
Mr Chips's Avatar
Rewards Points: 506
Why not Romex in Conduit?
I am planning to run power to my backyard tool shed, and in doing my homeowrk I see that you are supposed to use UF wire buried at 24" or STRANDED wire in conduit at 18"
almost everyplace i look it specifically says NOT to use romex in conduit, but it doesn't say why.
I plan on doing this right, so I will use stranded wire, but I am very curious as to the reason you aren't supposed to use romex, can somebody "shed some light" on this?
Mr Chips is offline   Reply With Quote
Old 11-07-2008, 08:46 PM   #2
Electrician
UF is allowed in conduit, but normal NM is not allowed in wet locations, conduit installed outdoors and underground meet this criteria.
Also, here are the depth requirements...
chris75 is offline   Reply With Quote
Old 11-07-2008, 09:25 PM   #3
The 2002 edition of the NEC can be interpreted as prohibiting the use of NM cable (Romex) in conduit. As I understand it, this was a result of miscommunication between the code-making panels that write the code, rather than a deliberate prohibition. The 2005 NEC clearly allows NM cable to be run in conduit. However, NM can't be used in wet locations. The inside of a conduit in a wet location is considered a wet location.
Matsukaze is offline   Reply With Quote
Old 11-08-2008, 09:58 AM   #4
Rewards Points: 160
While NM in conduit is allowed, it is not practical for most applications. It can't get wet and it is very difficult to pull multiconductor cables into conduit. Especially UF. Another thing to remember is that NM and UF have a large surface area, and could violate the conduit fill requirement. It's better to use individual conductors in conduit and if buried or outside the conductors must be rated for wet duty. THWN would most likely be what you will use. The "W" in the wire description is for wet locations. THHN is usually dual rated THHN/THWN.