Why Does #4 CU Have Different Ampacities? - Electrical - DIY Chatroom Home Improvement Forum
Old 11-04-2010, 02:13 AM   #1
Knothead
sandersdon's Avatar
Why does #4 CU have different ampacities?
Per tables 310-15 and 310-16:
#4 copper is rated at 100 amps when used as a service entrance (SE) but only 70 amps (60 C) when in NM-B cable. The wire is the same gauge so why the restrictions on ampacity?
Also, NM-B is not even listed in table 310-16. The insulation is PVC per the manufacturer but are the individual conductors considered any specific type (i.e. THHN, etc.)?
sandersdon is offline   Reply With Quote
Old 11-04-2010, 02:21 AM   #2
nap
You talking to me?
nap's Avatar
Rewards Points: 6,290
the size of the conductor is only part of the determination. The insulation further restricts the ampacity. Different types of insulation allow different ampacities.
Then, the use places other restrictions or alllowances of the ampacity.
to determine NM ampacity, go to the chapter on NM. It will tell you the ampacity is that in the 60 column of 310.16 but when derating, you can use the next column (75?) but the final figure cannot be any greater than the 60 column.
what the individual conductors are insulated with are irrelevant. It is rated as I stated and it doesn't matter what the insulation is. You cannot modify the rating or use based on the insulation of the individual conductors.
and if you were talkiing of 310.15(B)(6), that is a special exception basically due to the fact that residential services are not generally loaded to capacity so they allow a slightly undersized wire for such installations.
Old 11-04-2010, 02:40 AM   #3
Knothead
sandersdon's Avatar
Let me rephrase the question: (humor me please)
It seems to me a wire of a certain gauge will physically pass a certain amount of current regardless of the insulation type or thickness (as in a bare wire).
Isn't the insulation an electrical insulation as opposed to a thermal insulation? Obviously any thickness of insulation will have thermal properties but that isn't its primary function, is it?
I guess it's more of an electrical theory question rather than a code question.
Also, what is the reasoning for rating all NM-B at 60 C?.
Old 11-04-2010, 02:42 AM   #4
Knothead
sandersdon's Avatar
Also, it's late. Go to bed.
Old 11-04-2010, 02:49 AM   #5
nap
You talking to me?
nap's Avatar
yes
no and it isn't really a consideration.
the ability to withstand higher temps without degradation of the insulation is why one wire type will be rated a higher ampacity than another.
Not sure but I suspect it is because it is a cable where the outer sheath will retain heat. If so, it would be a derating by the code similar to the limitations that #10 wire be limited to 30 amp circuits, #12 to 20 amp circuits, and #14 to 15 amp circuits.
Old 11-04-2010, 02:50 AM   #6
nap
You talking to me?
nap's Avatar
It's only 3 am. I sleep until 8:30-9:00. That's 5 1/2 to 6 hours. Old people don't need as much sleep
either that or the fear of never waking up again keeps us awake
Old 11-04-2010, 06:33 AM   #7
Rewards Points: 1,418
There is also a greater number of amperes allowed when the wire is hung "in free air" such as between the house and the utility pole as opposed to in a cable or conduit in the wall. In the former case heat is dissipated more rapidly.
For a given wire size and material and a given number of amperes, the same voltage drop occurs and the same number of calories/BTU of heat are generated per foot of wire.
Old 11-04-2010, 06:59 AM   #8
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,822
The size of the conductor is only one part of several in the ampacity equation. Why do your think there are so many columns in 310.16 and differing numbers.
The setting and intended use are two main factors. IMO this is why NM is confined to 60 deg C. NM is typically installed in walls and ceiling that are insulated and attics which get very hot. SE cable is typically installed exposed.
Speedy Petey is online now   Reply With Quote
Old 11-04-2010, 11:04 AM   #9
Knothead
sandersdon's Avatar
Interesting. Thanks for all your replies. I hope y'all don't mind my curiosity - I always want to know why things are as they are.
Gauge Wire and Breaker Discrepancy broken_scout Electrical 26 12-22-2007 11:07 PM