Why Do I Have Voltage On Both Wires But No Lights - Electrical - DIY Chatroom Home Improvement Forum
Old 09-29-2007, 01:58 PM   #1
why do i have voltage on both wires but no lights
i went to turn on the lights in my livingroom but there was what appeared to be a surge and the lights went out in the livingroom and diningroom, so i went to reset the breaker but the breaker did not trip, so i remove the light switch and found 120 on both my hot and neutral, i checked my light fixture and i was reading the same 120 when checking to ground, and every outlet and every fixture was the same, why is this please help
kenny357 is offline   Reply With Quote
Old 09-29-2007, 02:16 PM   #2
When you say that you found 120 volts on both hot and neutral, do you mean that both hot and neutral had 120 volts over ground? Or do you mean there was 120 volts between hot and neutral?
NateHanson is offline   Reply With Quote
Old 09-29-2007, 02:53 PM   #3
i found 120 over ground
Old 09-29-2007, 02:58 PM   #4
so hot and neutral were BOTH 120 over ground?
Did you measure between neutral and hot?
Old 09-29-2007, 03:15 PM   #5
Electrician philosopher
Open neutral! Anybody?? I would shut off breaker and start checking the circuit.
Andy in ATL is offline   Reply With Quote
Old 09-29-2007, 03:23 PM   #6
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
Andy....Yes open neutral. Depending on his tester 120 volts neutral to ground is an expected reading. He has power to the receptacle so his branch circuit gounded leg (Neutral) is open. He needs to check as you advised. Probably a bad backstab on a receptacle.
Stubbie
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie