What's The Best Way To Splice 1/0 Cable? - Electrical - DIY Chatroom Home Improvement Forum
Old 01-18-2008, 08:09 PM   #1
Question
What's the best way to splice 1/0 cable?
I'm running a 100 AMP sub-panel 100' away from my main panel for an out building. I ran 1/0 direct burial 3-conductor cable to the site and allowed for enough cable to run up the wall into the new sub-panel.
For reasons to lengthy to mention, I must now locate the new panel an additional 20' away from it's intended location. What is the best way to extend this run?
1. A junction box with lugged connectors above ground? OR
2. Butt splices suitable for burial.
Thanks in advance for any recommendations.
Randell Tarin is offline   Reply With Quote
Old 01-18-2008, 08:11 PM   #2
3-conductor cable
Uh oh......3 conductor with ground?
Don't splice below ground unless you have to. Water happens. Take into consideration the conditions, grade etc. If it AL wire, forget underground.
220/221 is offline   Reply With Quote
Old 01-19-2008, 09:07 AM   #3
Re: What's the best way to splice 1/0 cable?
That really doesn't answer my question. How do I actually splice the cable?
As to the ground, this is a sub-panel. It will have an isolated ground attached to a grounding rod.
I'm not sure what your issues are with aluminum, but underground aluminum is regularly used in my area.
Old 01-19-2008, 09:29 AM   #4
Use big wire nuts. Just kidding. Relax for a second, he was just trying to get more information about the install. You say you're only running three wires to the building and that's a red flag that any electrician would question.
jerryh3 is offline   Reply With Quote
Old 01-19-2008, 09:35 AM   #5
Electrician philosopher
Polaris taps.
Andy in ATL is offline   Reply With Quote
Old 01-19-2008, 10:07 AM   #6
What are Polaris Taps?
Old 01-19-2008, 10:14 AM   #7
To Jerryh3: Must the sub panel be bonded to the main ground? I've been through this before when my main was wired.
I live in a cabin in the woods. My meter base sits atop a 200 amp service panel with pass-through lugs. This panel is grounded with a rod. A 3-conductor wire then feeds a 200 AMP panel at the house 300 feet away. It has its own grounding rod. Wouldn't what I'm doing on this current project be the same? I plan to have an isolated equipment ground in the sub that's bonded to it's own grounding rod.
Old 01-19-2008, 10:19 AM   #8
Polaris taps:
http://www.nsipolaris.com/pdf/polaris.pdf
Old 01-19-2008, 10:25 AM   #9
Rewards Points: 204
Article 300.5 (E), Allows splices underground without the use of an enclosure. However, the splices must be approved for the location and installed according to the splice manufacturers recommendations.
Crimp butt splices are what I would use. Make sure you use the right crimp tool/setting and correct insulating method as described by the manufacturer.
The other's are correct regarding the need for 4 wires. If you have two hots one neutral and one ground you are okay. If not, you can use an NEC exception making the sub panel a new service panel without the need for a another meter. (different subject).
Aluminum direct burial is also prevalent in my area for residential. What type of cable is this? It will marked on the jacket.
Andy.....Got any pics of the polaris taps. Never used them before. Thanks in advance....John
ps...Just saw the link. Go with Polaris. (Blue)
If it worked before you worked on it. You did something wrong.
Old 01-19-2008, 10:36 AM   #10
Exceptions 250.32(b)(2)?
Old 01-19-2008, 10:36 AM   #11
Rewards Points: 204
Randell. Looks like your cabin set up is the exception in the NEC for sub panels. They basically made both panels main service panels. I will have to look at the requirements to meet that standard. Someone here may have the requirements in their head.
Old 01-19-2008, 10:37 AM   #12
I had to go and look....
AWG 1/0 AL TYPE USE 2 80 MILS XLP INSULATION 600 VOLT
PHASE AAAAA DW
Old 01-19-2008, 10:40 AM   #13
Rewards Points: 204
Thanks jerryh3.
Old 01-19-2008, 10:51 AM   #14
nap
You talking to me?
nap's Avatar
Rewards Points: 6,290
as one poster stated, try to stay away from undeground splices. It is just trouble waiting to happen in the future. Even when done correctly, they tend to cause problems at times.
I would suggest not using polaris connectors unless you want to spend money. They are expensive and provide no real benefit for your situation. If available, I would use a crimp on splice but since this is a one time thing, obtaining the crimp tool may prevent this from being realistic. I am kind of cheap and would simply use split bolts if I could not use crimp on splices. Make it so your joints are in a j-box.
Old 01-19-2008, 10:56 AM   #15
Is there a j-box that has attached lugs for this purpose?
In-Floor Heating Cable Trouble... sootybuttercup Electrical 24 12-18-2014 08:01 PM
Projector Receiver cable TV box bigboyjoel Home Theater 4 12-19-2007 02:23 PM
four wires inside a cable?! joeyboy Electrical 23 11-05-2007 10:31 AM
Coaxial Cable Question bahaisamurai Home Theater 9 08-08-2007 02:54 PM
upgrading service cable Clutchcargo Electrical 1 06-22-2007 10:04 AM