-   -   What wire to use to run 300' for 110 service (http://www.diychatroom.com/f18/what-wire-use-run-300-110-service-38209/)
bobfake 02-12-2009 02:44 PM
My wife and I have a 2nd home and would like to run electricity from the house to the dock - which is approximately 300'. Initially, I will just have an outdoor quad receptacle and possibly a pole mounted light. Eventually, I may have more electricity requirements (boat house with lights/lift, gazebo with lights/fan, etc.), so I want to have enough electricity available for whatever needs I may have in the future.
What type of wire should I run for the 300' length? I have plenty of space in the breaker box and am using nothing close to the 200amp service.
Thank you very much!
jerryh3 02-12-2009 03:09 PM
What's your budget? If it were me, I would only want to dig this once. A 40-60A sub-panel would probably be the best thing to do right now.
bobfake 02-12-2009 05:37 PM
No specific budget and you are correct - I don't want to dig more than this one time. That's why I want to know what wire to run so I have plenty of room to grow.
I can get a trencher and do that myself. Let's assume a 60A subpanel. What specific wire do I need to run for that distance? I can lay the wire, etc and then have an electrician hook it up to the house panel and the new sub-panel.
jerryh3 02-12-2009 06:25 PM
I think #6 on a 50A breaker would be fine for what you're proposing. If you're going to have the electrician pull the permit, make sure you talk to him first before you buy anything for the project.
ctsmiths 02-12-2009 06:55 PM
If your going to run UF cable the voltage drop across 300' would put you out of the range of #6 (NEC 310.16, UF, 55A). Also 215.2 (A)3 fpn says NO larger than 5% voltage drop, #6 gives you 6% #4 gives 3.8%. I would go with #4 in pipe if money is not a problem. http://www.csgnetwork.com/voltagedropcalc.html
jerryh3 02-12-2009 07:09 PM
Not sure I understand what you're saying with this line. I agree about the VD at 50A, but the likelihood that the feeder would ever be loaded to that level is probably minimal.
Speedy Petey 02-12-2009 07:31 PM
I also agree that VD is certainly an issue at 300 feet, but it is NOT a code requirement to adhere to the 3% & 5% limits. It is just a suggestion.
At 300', using #4cu would be just at the recommended VD limit for a feeder with a continuous 40A load.
I doubt a feeder such as this would ever see 40A @ 240v continuous.
ctsmiths 02-12-2009 07:46 PM
Have you ever done VD cal before? You have to do it because of the lenght. The amperage increases as the voltage drops on the line, and by the nec you need to size the wire for the total possible amp draw on the line.
jerryh3 02-12-2009 07:54 PM
So, what would be the problem with 6/3 on a 50A breaker?
ctsmiths 02-12-2009 07:59 PM
I agree but being that it is near a body of water and the lenght involved Im sure that an inspector ( at least where I am located ) would want it done this way.
Speedy Petey 02-12-2009 08:00 PM
I'm really not sure what the water has to do with it, but I would it that way too. An inspector though would have a hard time making something stick that is NOT code required.
220/221 02-12-2009 08:00 PM
I'd run minimum #6's in 1" PVC and install a small 8 space sub panel.
I'd consider adding another 1" minimum conduit for phone/cable/communication wire.
No back to back tight 90's. Dig straight with gentle turns wherever possible.
ctsmiths 02-12-2009 08:01 PM
He is looking at a lot of load here with boat lift, and a boat house how could you say the load is not big enough?:confused1:
ctsmiths 02-12-2009 08:05 PM
There are also lots of other requierments for panels around bodys of water so be sure to consult with an inspector or electrician in your area before starting work!:thumbsup:
Speedy Petey 02-12-2009 08:07 PM
Most boat lifts I have seen were on 20A 240v circuits and not having much of a load.
There are also lots of other requierments for panels around bodys of water.....
Such as?