What Size Wire To Use - Electrical - Page 3 - DIY Chatroom Home Improvement Forum
Old 05-27-2012, 09:34 AM   #31
Missouri Bound's Avatar
Originally Posted by Marc Frederick View Post
I have to run a new circuit for a central air unit. The nameplate on the unit reads: 200/230 volts, minimum circuit amp 25, max fuse/ breaker 40, comp mot 18.6 RLA, o.d. Mot 1.4 FLA. any suggestions would be great. I'm thinking 8/2 wire but wanted to get other opinion. Thanks
Here's how I read it...a #10 wire is fine for a 25 amp circuit. Since it is a motor circuit, you can use a 40 amp breaker. # 12 wire would be close because the RLA on the compressor is what it could draw under some circumstances. Obviously a locked rotor would trip a 40 amp breaker before it could damage the wire, but running a 20 amp load on a #12 wire is not a good idea. Again, this is my opinion, and how I would wire this circuit.
Do you want it your way or the right way?
Old 05-27-2012, 09:36 AM   #32
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
you guys are not getting it, the manufacture ALREADY added 125% to that minimum circuit ampacity...nothing more needs to be done, #12 is perfectly fine for a 25 amp load...
And again, #12awg is actually rated for 25 amps... don't be scared of this fact.
And I doubt a locked rotor would trip the 40 amp breaker, because the thermal overload in the motor would kick in WAY before the thermal part of the 40 amp breaker...
The Following 2 Users Say Thank You to stickboy1375 For This Useful Post:
micromind (05-27-2012), mpoulton (05-27-2012)
Old 05-27-2012, 09:43 AM   #33
Guys it's Sunday I've got to get out of here.
I guess we could go on and on, but please give this some thought.
12 ga copper wire like Romex needs a 20 amp breaker. The device, appliance,etc. may have other wires inside it that uses different wiring size tables.
Electrician's wire these appliances, units, etc. per application.
Hope every one has a safe Holiday !
Kapriel is offline   Reply With Quote
Old 05-27-2012, 09:45 AM   #34
E2 Electrician
In certain applications, I agree, in others, I disagree.
The Following User Says Thank You to stickboy1375 For This Useful Post:
Old 05-27-2012, 09:46 AM   #35
Later guys, Got to go.
Old 05-27-2012, 09:50 AM   #36
E2 Electrician
Pretty picture to help see the light.
Old 05-27-2012, 10:27 AM   #37
Semi-Pro Electro-Geek
Rewards Points: 2,922
No, #12 wire requires whatever breaker size the NEC requires for the specific application. For this application, a 40A breaker is allowed. Read Article 440, or any of the numerous prior threads on here where this issue has been beaten to death. The summary is this: the "typical" wire/breaker combinations do not apply strictly to HVAC, motor, and welder circuits. For those circuits, the wire can be sized to the LOAD, which has internal overload protection, and a larger breaker can be used to handle momentary surges of higher current.
This is a 20A load according to the nameplate, so #12 wire is just fine. A 40A breaker is allowed for this #12 wire, both according to the nameplate and also according to Article 440.
mpoulton is offline   Reply With Quote
The Following 3 Users Say Thank You to mpoulton For This Useful Post:
Jim Port (05-27-2012), micromind (05-27-2012), stickboy1375 (05-27-2012)
Old 05-27-2012, 11:33 AM   #38
Idiot Emeritus
Rewards Points: 1,492
Article 440 in the code covers Air Conditioning And Refrigeration Equipment.
Part III of Article 400 is entitled "Branch-Circuit Short-Circuit and Ground-Fault Protection.
440.21 "The provisions of part III specify devices intended to protect the branch-circuit conductors, control apparatus, and motors in circuits supplying motor-compressors against overcurrent due to short circuits and grounds. They are in addition to or amendatory to the provisions of Article 240.
Article 240 is entitled "Overcurrent Protection".
240.4(D) Small Conductors. Unless specifically permitted in 240.4(E) or 240.4(G), the overcurrent protection shall not exceed 15 amperes for #14 AWG, 20 amperes for #12, and 30 amperes for #10 copper.
Table 240.4(G) lists Article 440 parts III and IV.
Therefore, the 20 amp rule for #12s does not apply to HVAC equipment. This is stated further by 440.21
Rob
micromind is offline   Reply With Quote
The Following User Says Thank You to micromind For This Useful Post:
Old 05-27-2012, 06:08 PM   #39
I stand corrected.
Thank you Stickboy for the pretty picture, I always like those.
Thanks also to Micromind and mpoulton.
I wouldn't of believed it if I didn't see the NEC photo.
So I'm guessing the NEC will allow a 40 amp breaker in a CB panel lets say 75' away in the basement to serve as protection for the branch circuit and then another 40 amp breaker at the HVAC unit.
Old habits are hard to break, but I learned something today.
Thank you all for the work to explain this to me.
I owe you all.
The Following 2 Users Say Thank You to Kapriel For This Useful Post:
Old 05-27-2012, 06:10 PM   #40
E2 Electrician
I stand corrected.
I owe you all.
I don't use fuses or circuit breakers at the disco for the AC unit,(unless required) I just install pullout style disconnects, but yes, you could have 40 amp breaker at the outdoor unit.
Old 05-27-2012, 06:11 PM   #41
Licensed electrician
Rewards Points: 1,490
There would be no need for two breakers in the circuit. One at the panel would be enough. The unit only needs a means to disconnect the power for servicing.
Old 05-27-2012, 06:13 PM   #42
E2 Electrician
I stand corrected.
I owe you all.
Don't worry about it, you are not alone in this territory, I work with guys all the time and they freak out when I tell them it's safe. I don't know what people learn in the trade, but its nothing to do with motors I can tell you that much.
Old 05-27-2012, 06:26 PM   #43
Idiot Emeritus
Originally Posted by stickboy1375 View Post
Don't worry about, you are not alone in this territory, I work with guys all the time and they freak out when I tell them its safe. I don't know what people learn in the trade, but its nothing to do with motors I can tell you that much.
And I'd bet you've seen more than one inspector who doesn't understand this as well.
I know I have!
Old 05-27-2012, 06:34 PM   #44
E2 Electrician
I know I have!
Yep, and its a pain to teach someone thats adamant on being correct because he has this title of "inspector" heaven forbid someone learn something, pride has to be the hardest thing to swallow ever!
Old 05-28-2012, 09:37 AM   #45
Smaller wire has more resistance. A motor at a standstill is more of a resistor than an inductor. Therefore its current draw will depend almost entirely on the voltage at its terminals.
Since there's more resistance in a smaller wire, there will be less voltage at the motors terminals, therefore less current.
Less current will result in less voltage drop at the panel.
The difference between #12s and #10s on a 75' run is pretty small, but it could easily make the lights dim noticeably less.
If you'd like, I can run some numbers and see what comes up, but without the locked-rotor current curve, I'd be guessing to some degree.
Rob
Even with connecting wire of zero resistance, at 40A the 240 volts at my panel would drop 40 x .02 = 0.8V. Not much dimming for the rest of the house.
Ground Location and Wire Size LHB_Texas Electrical 25 05-27-2011 09:38 AM
wire size for 160' feeder to subpanel steveski Electrical 3 05-21-2011 09:41 AM
HALP! Master/Remote Dimmer troubles! Confuserated Electrical 9 02-12-2010 03:30 PM
hooking up dryer....bronx ny code SURFBUG Appliances 6 10-14-2008 09:41 PM
Wire size and Breaker size for remodel ?? Skydmark1 Electrical 12 12-15-2007 05:00 PM