What Size And Type Wire Should I Use? - Electrical - DIY Chatroom Home Improvement Forum
Old 06-19-2010, 06:38 AM   #1
What size and type wire should I use?
I'm looking to run an outlet(to run a battery charger or radio) and couple of lights(one light would be a 500w flood light the other would be just a 60w bulb) from my house to a gazebo 350' away. I'd bury the wire, and plan on putting it in PVC conduit. What type and size wire should I use for this project?
Iman is offline   Reply With Quote
Old 06-19-2010, 07:05 AM   #2
The smallest circuit you can run for an outlet is a 15A, #14 wire. But at that distance, I would use #12. Single conductor wires are needed in a conduit, as opposed to an MM cable.
The Following User Says Thank You to Just Bill For This Useful Post:
Iman (06-19-2010)
Old 06-19-2010, 07:16 AM   #3
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,878
Personally I'd go with #10 or #8 and run a multi-wire branch circuit.
For one, a MWBC will lessen the problem of voltage drop, and second, you never know what someone will plug in down there, so wire it as if someone will be using a circular saw some day.
The Following User Says Thank You to Speedy Petey For This Useful Post:
Iman (06-19-2010)
Old 06-19-2010, 01:38 PM   #4
Master Electrician
i'm not sure what the voltage drop limits are in the states but #10 comes in a 5.8% and #8 comes in at 3.7%. You would have to use a #8 in canada i believe.
i'd put a 1" pipe in. Just makes life easier :D
andrew79 is offline   Reply With Quote
Old 06-20-2010, 02:57 AM   #5
" Euro " electrician
frenchelectrican's Avatar
Andrew79.,
Typically in the States we will figure the VD to max of 5% but 3% is most common numbers there are few case it can have more than 5% but it is very I will repeat this very rare.
To OP
Just stick with 6.0mm˛ or 10mm˛ { #10AWG or #8 AWG } and run in multicircuit fashion and yeah of course you will need RCD { GFCI } recepetale at the end of run { don't bother use the RCD breaker due the distance it can make a false trip unless you have it in the subpanel }
The reason why as SpeedyPete mention one item and also some case someone bring the monster sized boom box to crank up a bit that can take some bit of serious juice as well.
Merci,Marc
Size wire for A/C, A/H and Range? tripflex Electrical 6 06-07-2010 11:38 AM
Size and type of entrance wire for 200A? Beemer533 Electrical 7 03-15-2010 11:54 PM
Size of Wire & type of wire agman Electrical 6 11-10-2009 09:13 PM
Please confirm wire size and type for amperage. wantsomegetsome Electrical 14 05-07-2009 06:49 AM
Wire size and type in Rigid Metal Conduit Al the Diy guy Electrical 5 02-05-2008 09:31 PM