Originally Posted by Toller View Post
For bonus points, if someone wants to explain how a 3hp motor can draw 20a, I would like to know. I thought maybe that was with no load, but it is 20a while working the machine. Seems really really high.
Sounds about right !
1 hp = 750w.
3 x 750 = 2250w.
2250w / 120v = 18.75a.
Close enough !
dmxtothemax is offline   Reply With Quote
Old 01-17-2013, 05:49 AM   #17
MEASURE ONCE, CUT TWICE
123pugsy's Avatar
Rewards Points: 416
Thats interesting. I can use #12 and a 40a breaker if I hardwire. There would only be about 25' for cable, so the voltage drop would be trivial. I think a 40a breaker is overkill; I can use a 30a breaker can't I?
I know I can't just run the romex to the switch box; I would have to run romex to a junction box and run some sort of whip to the switch box. What are the requirements for that?
I take it that everything changes if I go to a plug. What do I need then?
I appreciate the help.
Last time I checked, #12 needs to be protected by a maximum 20 amp breaker.
I would use emt if surface mounting, from the panel to a box and cabtyre for your "whip" to the motor.
123pugsy is online now   Reply With Quote
Old 01-17-2013, 08:01 AM   #18
Rewards Points: 720
What did you "check" to find that? That is a common misconception among DIY'ers who don't read the ENTIRE code.
Mark
busman is offline   Reply With Quote
Old 01-17-2013, 01:21 PM   #19
123pugsy's Avatar
Rewards Points: 416
Mark
Thanks for pointing out my error.
Enlighten us DIY'ers as that's why we're here.
Thanks.
Pugsy
Old 01-17-2013, 01:50 PM   #20
Semi-Pro Electro-Geek
Rewards Points: 2,858
Thanks.
Pugsy
Stickboy's post #9 above cites the code sections and includes a diagram.
I am a lawyer, but not your lawyer. And who cares anyways? We're here to talk construction. This is DIY advice, not legal advice.
mpoulton is online now   Reply With Quote
Old 01-17-2013, 02:47 PM   #21
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
Originally Posted by stickboy1375 View Post
You size the OCP and min. branch circuit wiring off the HP rating...
3 HP @ 240 v. = 17 AMPS
17 AMPS X 250% = maximum breaker size, = 40 Amp breaker
17 AMPS x 125% = minimum branch circuit wiring, = 21.25 #12AWG is good for 25 amps in this scenario,
This of course is for hard wiring the motor.
THHN/THWN in conduit yes. Romex is only good for 20A 60C. 2011 NEC.
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
The Following 2 Users Say Thank You to electures For This Useful Post:
frenchelectrican (01-19-2013), stickboy1375 (01-17-2013)
Old 01-17-2013, 03:09 PM   #22
Rewards Points: 948
Is MC considered to be in conduit?
Toller is offline   Reply With Quote
Old 01-17-2013, 04:46 PM   #23
Nope. MC is MC - it's a specific type of cable assembly, like NM or UF. THWN in FMC may seem almost identical to MC, but according to the code it's completely different.
The Following User Says Thank You to mpoulton For This Useful Post:
electures (01-18-2013)
Old 01-17-2013, 05:59 PM   #24
Rewards Points: 948
Okay, will this work?
I have a 25' length of 10/3 romex. Can I just ignore the unneeded wire? I don't expect to ever use it for any thing else, so I might as well use it here. I would run it from the panel box to a junction box above the cyclone.
Also I have a 12' length of 10/3 SOOW. Can I run that from a junction box to the switch box on my cyclone? I used it to connect a generator to a transfer switch, but don't have either of them anymore.
Now I just have to decide on the breaker. My understanding is that I could use either a 30a or a 40a. I think a 30a will be adequate, but mfg. recommends a 40a presumably to avoid nuisance trip on startup, but I have pretty much determined that is not a problem. Would a 40a be any more dangerous? Just about anything dangerous that would trip a 30a would trip a 40a also. It is all so confusing, but I think I am almost there.
Old 01-17-2013, 06:52 PM   #25
30A on #10 wire is definitely fine for this installation. Since that does not rely on the motor's thermal cutout for overcurrent protection (#10 wire is rated for 30A), you can install a receptacle and put a plug on the dust collector if you want. I would install a 4-wire 30A dryer receptacle next to the machine, and put a standard dryer cord on it. Leave the white wire unconnected (taped off) at the machine.
Old 01-18-2013, 08:37 AM   #26
electures's Avatar
Yes, you can use the 10/3 and abandon the un used wire. Just cap it off. As for the SOOW cord, splicing it in a JB makes it a permenant wiring method. That's a no no.
Old 01-18-2013, 03:01 PM   #27
Rewards Points: 948
Geez, just when I thought I had it settled.
What material is proper from the junction box to the tool?
Is MC acceptable?
I know I can use a 40a with the #10 wire if it is permanent. Is that true for the plug/outlet also?
Old 01-18-2013, 03:40 PM   #28
123pugsy's Avatar
Rewards Points: 416
Is MC acceptable?
A power tool or machine is not a part of a structure. Does that not mean that the cord is OK to use? Isn't the only part of this run considered permanent, the run from the panel to the JB?
Or if splicing into the JB does make it permanent and unaccepable, would adding a recepticle in the JB and a plug on the end of the cord be good?
Old 01-18-2013, 05:39 PM   #29
The cord is fine if it's plugged into a receptacle, but not if it's wired in. But if you use a receptacle, there is a good argument that the breaker and wire size must match (i.e. 30A for #10) since it is now a general-purpose receptacle circuit and not a motor load circuit.
Need a wiring diagram Mooreski Electrical 47 02-01-2015 04:07 PM
proper calculation for circuit size withoutlicense Electrical 19 02-16-2012 10:15 AM
Can someone help me size my lighting circuit? Alan Electrical 12 01-19-2012 10:01 AM
Just for fun Andy in ATL Electrical 56 10-20-2009 10:33 AM
Circuit breakers and wire size stan 41943 Electrical 19 03-06-2008 03:29 PM