What size breaker and wire ?
Hi
I am new to electrical stuff and have a fairly simple question. I have a out building that i plan on running outlets and lights too. 1. What I need to know is what size breaker is appropriate for my application? 2. What is the size of the wire that I need to use to go from my main panel in my house to my out building (ie 6,8 gauge) ? This wire will be running underground for approximately 20' and the total distance from my main panel to the building is 85 '. This is what I will have in my building for outlets and lights: - 14 total outlets (110v) - 3 standard strip lights This is what my tools or devices are: - heat gun - battery chargers - full size freezer - sealing iron - small heater (1500 watt) - 3 strip lights - pedestal fan - dremel tool - drill I do not plan on using more than 4 things at one time excluding my lights if this helps ! Any help would be greatly appreciated ![]() Thanks Scott |
|
|
|
|
|
#2 | |
|
Member
Join Date: Aug 2010
Location: Canada, PEI
Posts: 37
|
What size breaker and wire ?Quote:
Seems like a lot of outlets for a building. But what I would recommend is perhaps putting a sub panel in your building Dedicated 20amp circuit for the heater 12/2 Dedicated 15amp circuit for the deep freezer 14/2 Two additional 15amp circuits with the remaining outlets split between them 14/2 1 15amp circuit for the lighting 14/2 You could use a 60amp subpanel fed with #6 copper Check with your local electrical codes but this should help start you out. |
|
|
|
|
|
|
#3 |
|
Member
Join Date: Sep 2008
Location: Massachusetts
Posts: 256
|
What size breaker and wire ?
I also would recommend #6 wire and a 60 amp sub panel.
|
|
|
|
|
|
#4 |
|
Newbie
Join Date: Feb 2011
Posts: 2
|
What size breaker and wire ?
Hi
Thanks for the idea for the sub panel. The problem I have with putting a sub panel in is that I would need to have another service run out to that sub panel and hence another electrical bill. I plan on expanding my main house panel to a 200 amp panel and going that route. If I was to do this could i use a 60 amp breaker in my new house panel or would I have to use more than one ? Thanks Scott |
|
|
|
|
|
#5 | |
|
Just call me Andrew
Join Date: Mar 2009
Location: Albany, NY
Posts: 2,247
|
What size breaker and wire ?Quote:
What size is your current house panel? 100A? You probably do not need to expand your current panel unles your calculated load is nearing 100A, which it likely is not.
__________________
Andrew |
|
|
|
|
|
|
#6 | |
|
Member
Join Date: Jun 2007
Location: South Carolina
Posts: 3,349
|
What size breaker and wire ?
Use a 70 amp or higher main breaker sub panel. You can feed it with any size circuit you want.
Quote:
From reading your equipment list you would be foolish to not install the sub panel. Do it right the first time. Use PVC conduit and seperate wires. Four wires to be exact. H-H-N-G. |
|
|
|
|
|
|
#7 |
|
Member
Join Date: Nov 2007
Location: Nashua, NH, USA
Posts: 6,775
|
What size breaker and wire ?
One double wide two handled 60 amp breaker is all you need in your main panel. From there #6 copper wires to your outbuilding would be perfect.
By the way you are only allowed to have one power feed going out there. If you ran a thinner wire and later decided you need more power, you would have to start from scratch and decommission the old thinner wire. f you temporarily use 20 amp breakers (same double wide two handled) in your main panel you could procrastinate on putting a subpanel in the outbuilding and still have the #6 wires for future power needs.
__________________
The average homeowner who lost his house in the Oklahoma tornadoes should move for good and not rebuild. Too much complexity watchdogging the contractor. Too much a chance to be defrauded. |
|
|
|
![]() |
| Thread Tools | Search this Thread |
| Display Modes | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Wiring Size Calculations for New Service | CorinthWest | Electrical | 7 | 12-07-2010 12:36 PM |
| need help getting right size breaker and wire for tig welder | jss12 | Electrical | 11 | 10-18-2010 03:49 PM |
| hooking up dryer....bronx ny code | SURFBUG | Appliances | 6 | 10-14-2008 10:41 PM |
| Wire size and breaker discrepancy | Randell Tarin | Electrical | 22 | 04-10-2008 08:03 PM |
| Wire size and Breaker size for remodel ?? | Skydmark1 | Electrical | 12 | 12-15-2007 06:00 PM |