What size braker should I use?
I am running a new outlet for my plasma cutter (see details below). I had been using it on a regular outlet, but it would often trip the breaker so I am now running a new outlet for it. I bought a new plug for the plasma, receptacle, and I bought some 12-2 wire. I was in a hurry and couldn't find anyone at Lowes that was worth a hoot to ask about a breaker. What would you guys recommend?
Plasma details:
This machine has exactly the same parameters as the Plasma-Tec40SV with an additional feature that allows it to operate on 90 to 260 volts AC single phase, which makes it very versatile. As a worst case test we connected it to 110volts through a common 6 ft extension cord and was able to cut 1/4" steel. Do to it's efficiency it is useful even in a worst case power situation. It only weighs 20 lbs. and is about the size of a small breadbox. Just tote it around and plug it in anywhere... your in "go-mode" with this machine!
chopshop is offline   Reply With Quote
Old 08-12-2010, 07:20 PM   #2
Rewards Points: 6,652
What does the plate on the equipment state?
Old 08-12-2010, 07:21 PM   #3
Electrician
Proby's Avatar
The 40SV lists the following:
40 Amp, 220 Volt, Single Phase, Input Current Maximum: 22 Amps, Duty-Cycle: 60% at Full Power, 100% at Three Quarter Power
What type of plug was originally on the unit? I need better information, does the unit have a metal plate with ratings on it?
Anything fun is either illegal, immoral, or fattening.
Proby is offline   Reply With Quote
Old 08-12-2010, 07:39 PM   #4
When I bought it it didn't have one since you could pick, I just put a standard 110 plug on. Now I want to change.
Old 08-12-2010, 07:45 PM   #5
Old 08-12-2010, 10:44 PM   #6
" Euro " electrician
frenchelectrican's Avatar
I read the nameplate it say 5.1 KVA so you will need 30 amp breaker at 240 volts { two pole breaker }
I know the unit is rated at 21 amps per nameplate but if the unit have 30 amp 240 volt plug then you will need 30 amp breaker for this one.
Merci.
Marc
Old 08-12-2010, 11:12 PM   #7
Electrician
Proby's Avatar
chopshop, what type of plug did you buy?
You'll need #10 wire to use along with a 30amp receptacle and matching plug for the plasma cutter.
Old 08-13-2010, 11:52 AM   #8
I think it's a 6-20r.
Old 08-13-2010, 12:54 PM   #9
Originally Posted by chopshop View Post
[SIZE=2]I had been using it on a regular outlet, but it would often trip the breaker
What duty cycle were you running?
How much off time between usages?
These values will give you some idea of how much bigger you have to go.
Some welders get incredible peak power and high average power out of a wall outlet but it is a close match between the breaker trip curve and duty cycle and off times and the length/gauge of the connecting cord. The manufs seem to be making mostly true assumptions about resi. breakers.
Old 08-13-2010, 12:59 PM   #10
Originally Posted by Yoyizit View Post
What duty cycle were you running? How much off time between usages? These values will give you some idea of how much bigger you have to go.
I am not sure, it was at my shop. Anytime someone was using somthing when the plasma was running it would trip. I moved out of the shop and working out of my basement and garage.
Old 08-13-2010, 05:48 PM   #11
Electrician
Proby's Avatar
So you are going to need to get #10 wire, a 30A plug, and a 30A receptacle.
Old 08-13-2010, 09:06 PM   #12
From your posted diagram,
this thing draws current in pulses.
Breakers respond to RMS values, mostly. If you need to do troubleshooting with your setup you will need an ammeter that reads "true RMS".
Size of whole house fan needed Doug Crf General DIY Discussions 20 02-25-2011 11:29 PM
Determining Boot/Register Size Earnie HVAC 15 12-31-2009 05:00 PM
Building a patio cover...span and size of lumber Q's jongordo8 Building & Construction 1 08-30-2009 12:08 AM
pre-hung door, 32x80 is that door size or total size? RyanD Building & Construction 3 06-28-2009 10:33 PM
Room size X floor tile size deck hand Flooring 4 04-08-2009 04:42 PM