What Should I Use To Sexure Flex Conduit... - Electrical - DIY Chatroom Home Improvement Forum
Old 03-18-2009, 09:18 PM   #1
What should I use to sexure flex conduit...
I have 3/8 flex conduit I need to secure to a brick wall, the problem I have is finding a strap or device to secure the conduit to the wall. I can only find sizes from 1/2.
Should I ditch the 3/8 and go 1/2?
rgsgww is offline   Reply With Quote
Old 03-18-2009, 09:22 PM   #2
ive never seen 3/8 flex conduit...is it listed for what you are using it for?...i don't know, i'd probably just use 1/2
NolaTigaBait is offline   Reply With Quote
Old 03-19-2009, 12:33 AM   #3
Rewards Points: 2,350
Look harder. Home Depot and Lowes both have 3/8" straps. They may be in the section for bx/ac/mc fittings area.
Old 03-19-2009, 05:09 AM   #4
Rewards Points: 150
Send a message via AIM to Bocolo
http://www.homedepot.com/webapp/wcs/...atalogId=10053
One Pound of Knowledge Requires Ten Pounds of Common Sense In Order To Be Useful
Bocolo is offline   Reply With Quote
Old 03-19-2009, 07:04 AM   #5
Alright, I will look harder. Sometimes they stock the times all over the place so its hard to find what your looking for.
Thanks for the help.
Old 03-19-2009, 08:03 AM   #6
Electrical Contractor
350.20 States that you can't use anyting under 1/2 inch.
Use 1/2" PVC.
hpp58 is offline   Reply With Quote
Old 03-19-2009, 10:00 AM   #7
Use 1/2" PVC.
You are in the wrong article. Try 348.
Old 03-19-2009, 10:28 AM   #8
DIY'er
jamiedolan's Avatar
Rewards Points: 1,024
http://www.lowes.com/lowes/lkn?actio...20Hole%20Strap
Jamie
Jamie Dolan - Neenah, WI
Jamie Dolan Paw Dogs
Need Help Uploading Photos? Click here.
jamiedolan is offline   Reply With Quote
Old 03-19-2009, 10:57 AM   #9
Originally Posted by jamiedolan View Post
Thanks for the link.
Maybe I can get a list of everything I will need because lowes, menards, etc. are far away...
Old 03-19-2009, 11:01 AM   #10
Rewards Points: 246
348.20 Size.
(A) Minimum. FMC less than metric designator 16 (trade
size 1⁄2) shall not be used unless permitted in 348.20(A)(1)
through (A)(5) for metric designator 12 (trade size 3⁄8).
(1) For enclosing the leads of motors as permitted in
430.245(B)
(2) In lengths not in excess of 1.8 m (6 ft) for any of the
following uses:
a. For utilization equipment
b. As part of a listed assembly
c. For tap connections to luminaires (lighting fixtures)
as permitted in 410.67(C)
(3) For manufactured wiring systems as permitted in
604.6(A)
(4) In hoistways as permitted in 620.21(A)(1)
(5) As part of a listed assembly to connect wired luminaire
(fixture) sections as permitted in 410.77(C)
(B) Maximum. FMC larger than metric designator 103 (trade
size 4) shall not be used.
FPN: See 300.1(C) for the metric designators and trade
sizes. These are for identification purposes only and do not
relate to actual dimensions.
Table 344.30(B)(2) Supports for Rigid Metal Conduit
Conduit Size
Maximum Distance
Between Rigid Metal
Conduit Supports
Metric
Designator Trade Size m ft
16–21 1⁄2–3⁄4 3.0 10
27 1 3.7 12
35–41 11⁄4–11⁄2 4.3 14
53–63 2–21⁄2 4.9 16
78 and larger 3 and larger 6.1 20
Use 1/2". I failed an inspection one time because I used 3/8 to feed a water cooler.
Old 03-19-2009, 11:18 AM   #11
Originally Posted by J. V. View Post
348.20 Size.
430.245(B)
following uses:
604.6(A)
Conduit Size
Maximum Distance
Between Rigid Metal
Conduit Supports
Metric
1621 1⁄23⁄4 3.0 10
27 1 3.7 12
3541 11⁄411⁄2 4.3 14
5363 221⁄2 4.9 16
Its going to feed a furnace, so I'm going to go for 1/2.
Old 03-19-2009, 11:18 AM   #12
Sorry my bad.
Old 03-19-2009, 11:27 AM   #13
DIY'er
jamiedolan's Avatar
I am very lucky, A 20 minute drive from home puts me at Lowes, Menards, or Home Depot, and they are all close to each other.
I guess you can always order online.
Jamie
Old 03-19-2009, 11:30 AM   #14
DIY'er
jamiedolan's Avatar
Isn't a furnace exposed? Wouldn't it require EMT or other conduit system that is rated to provide protection from physical damage. I remember asking KC one time about using a BX whip to my furnace and he said it should not be allowed. So I replaced it with EMT.
EMT is getting really cheap, under $2 for 1/2" now.
Jamie
Old 03-19-2009, 11:39 AM   #15
Its tucked between the furnace and the wall, not sure if its considered exposed. I could try emt.
Its about a 30 min drive to those places, guess I just don't like going there.