What SE Wire (new Service) - Electrical - DIY Chatroom Home Improvement Forum
Old 08-22-2012, 10:35 PM   #1
Rewards Points: 91
What SE Wire (new service)
we are setting up our newly placed manufactured home, and are going to run the service entry wire ourselves. The meter will be a single phase, however the connection on the house states 3 phase 4 wire 60hz and 200amp. I was wondering if it was easy for an electrician to convert this.
Also I am wondering what is the best type of wire to use that won't break the bank. It will be about 200 feet meter to house, so is it best just to run 3 individual wires to the house? Also what size conduit?
no_Wedge is offline   Reply With Quote
Old 08-22-2012, 10:58 PM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 482
I'm pretty sure it does not say 3 phase.
jbfan is online now   Reply With Quote
Old 08-22-2012, 11:22 PM   #3
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
If you have so many uncertainties, why do this yourself?
Old 08-23-2012, 06:16 AM   #4
Rewards Points: 91
it says 3 pole actually
3pole 4wire 60Hz 200 amp
and i'm not connecting the wires to the house , I am just wanting to run the cable as it would cost a lot more for someone else to run it.
Old 08-23-2012, 06:53 AM   #5
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,214
You plan on running a service over 660 feet? You need the POCO to install a transformer closer to the house.
Coastal South Carolina
rjniles is offline   Reply With Quote
Old 08-23-2012, 10:18 AM   #6
Rewards Points: 160
That makes much more sense and it is still not 3 phase.
When you say "manufactured" what exactly do you mean?
Are they bringing in sections of the house to be erected on site? Or are they rolling it onto the property.
There is a big difference between a trailer and a manufactured or pre-fabed home. A very big difference.
Old 08-23-2012, 07:42 PM   #7
Rewards Points: 91
it's not modular, it's a solitaire mobile home, and it's already been set in place.
and no it's not over 660 feet. It's about 200 feet from the transformer they are installing.
Old 08-23-2012, 07:50 PM   #8
Missouri Bound's Avatar
Does this help? Wire ampacity chart
Do you want it your way or the right way?
Old 08-23-2012, 08:00 PM   #9
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
In order to answer this correctly I want to be sure of what you have by saying mobile home. So I'm attaching a image. tell us if that is what you mean by mobile home.
Some more questions ..
Pad mount transformer or up on a pole?
Where is the service equipment (main disconnect enclosure) and meter ? Usually for a mobile home there is a pedestal approx. 30 feet from the home then you run a feeder from that to the distribution panel in the home.
Old 08-23-2012, 08:04 PM   #10
kbsparky's Avatar
Mobile homes require the service equipment to be mounted away from the home -- usually on a separate pedestal. You can NOT mount the meter box on the house.**
The service pedestal must be within 30 feet of the exterior of the home.
If your meter and service disconnect is further away from that, then you have to install a separate disconnect box within the required 30 feet.
From there, you will need to use a 4-wire feeder into the home. Aluminum "mobile home feeder" cable is usually sufficient, with #4/0 hot conductors, and #2/0 neutral, and a #4 ground wire. All the conductors must be insulated.
This stuff may also be referred by some as "URD" cable.
**There are exceptions to this rule if the house is set upon a permanent foundation, and is reclassified as a "manufactured" or "modular" home.
-KB
Old 08-23-2012, 08:18 PM   #11
Rewards Points: 91
Stubie that is what i mean by mobile ( it is placed on a cinderblock foundation). The power company has the transformer on the pole, and will be installing the main disconnect with meter on the same pole (which is ~200 feet of wire) to the house pane.
Old 08-23-2012, 08:45 PM   #12
Rewards Points: 91
can't you run the wire directly from the breaker at the pole to the mobile home without another breaker? maybe using 4 wire feeder?
like this part number 540-6800J
Old 08-23-2012, 08:54 PM   #13
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,956
You HAVE to run a 4-wire feeder to a mobile home.
Is this REALLY a place you should be cheaping out on??? Why not just let your electrician do this so it will be done right?
The Following 2 Users Say Thank You to Speedy Petey For This Useful Post:
frenchelectrican (08-23-2012), Jim Port (08-23-2012)
Old 08-23-2012, 09:09 PM   #14
Rewards Points: 91
well my electric is on a coop, and there are no regulations out here past the meter. what I am asking, is if it would be necessary to add another disconnect box near the house?
Or just run the 2 hots 1 neutral, and 1 ground from the disconnect at the pole?
Old 08-23-2012, 09:10 PM   #15
UAW SKILLED TRADES
Stubbie's Avatar
There is more to this than you might think. Considering an electrician is a good idea. He can contract the trenching as I'm assuming your going underground.
Anyway use aluminum wire called mobile home feeder. It's 4 wires as KBSparky has already outlined.
As for going directly from the meter and disconnect on the pole to the panel in the mobile home I don't think they will let you. Have you talked to the inspectors about what is required for your situation ?
Direct burial wire for 100 amp service caugen Electrical 4 01-03-2017 07:53 AM
service entrance wire michaeljack Electrical 4 10-27-2011 12:25 PM
ceiling fan wicked97 Electrical 4 08-21-2011 08:12 AM
New upgraded 200A service wire connections WillK Electrical 1 04-28-2011 02:02 PM
Can I wire a new panel without service or run a "big" subpanel? tigereye Electrical 7 03-03-2009 04:00 PM