i have a GFI outlet on my front porch, it worked just fine. is on its own circuit except for a light in the basement, and it didn't have a ground. yesterday i replaced the old wiring with some romex that has a ground. now, the outlet keeps tripping, though i got it to stay 1 time. retesting made it go back to tripping. on the outlet itself, it says "white" and "hot", so that is how i wired it.
also, i tagged off of this outlet a wire that will be used for the front door lights. the wire is capped off.
i am :confused1::001_unsure:
k_buz 11-04-2012 08:47 AM
New GFI's will not reset if they are wired incorrectly. How did you "tag off this outlet" for a future light? Do you have line and load reversed?
Fix'n it 11-04-2012 08:55 AM
ok. but then why did it reset one time ?
it has 2 sets of screws.
well, it say white and hot on the back of the outlet. so i put the white wires on the white side, and the black wires on the hot side.
joecaption 11-04-2012 09:00 AM
There should have been a yellow sticker over the load side of the outlet.
There's also line and load molded right into the back of the outlet.
Line is incoming power, load is power going out.
Black wire on gold screw.
Fix'n it 11-04-2012 09:06 AM
yes, there was. i didn't know that there was an actual "in and out".
does that mean the gfi will protect the future lights ?
iirc, all the screws are white
k_buz 11-04-2012 09:14 AM
It probably didn't actually reset, the button just pushed in. The top terminals are usually the load side and the bottom are usually the line. You must keep the line/load wires together.
Fix'n it 11-04-2012 09:30 AM
it actually did. i had a tester plugged into it.
anyway. i probably wired it wrong, and i will correct it later.
ddawg16 11-04-2012 11:01 AM
Just to help clarify.....
You have a line side and load side.
The line side is where you connect your incoming power. At this point, you can use the outlet....and the test/reset should work.
If you want to connect additional devices that will be GFIC protected, you connect them to the load side. Those load side terminals are in parallel with the recept contacts.
Note...one of the most common wiring mistakes is for people to wire nut all the neutrals together.....including the load side. The load side neutral MUST connect to the neutral screw on the load side....
Fix'n it 11-04-2012 07:32 PM
i had it wired wrong. it is working correctly now. thanx fella's.