What Gauge Wire - Electrical - DIY Chatroom Home Improvement Forum
Old 07-28-2010, 05:43 PM   #1
Post
what gauge wire
hi i am wiring my detached garage (in canada) i am puting a 100 amp sub panel in the garage. i was told i need a smaller breaker in the main panel so i am using a 60 amp d.p.b. in the house witch should be sufficent for the garage. i have a run of a little less than 35 feet i was told i need to use #6/3 underground wire is this corect or can i use #8 or #10 i am running it in conduit underground
james582 is offline   Reply With Quote
Old 07-28-2010, 06:02 PM   #2
Electrician
Rewards Points: 770
#6 RW90(red, black, white, they have to be these colours you can't retape them) and a #10 green insulated ground conductor. You are best to install individual conductors if you have a conduit. If your going to use a cable you will have to use 6/3 NMWU.
darren is offline   Reply With Quote
The Following User Says Thank You to darren For This Useful Post:
james582 (07-28-2010)
Old 07-28-2010, 10:36 PM   #3
thank you verry fast and informitave
Old 07-28-2010, 10:45 PM   #4
last minute thought what size conduit should i use if im using plastic conduit
Old 07-29-2010, 09:01 AM   #5
Just call me Andrew
Rewards Points: 1,020
If you use individual THWN wires (three #6 and one #10), according to this raceway fill calculator, you need 3/4" minimum for sch. 40 pvc. I'd run 1" to make it easier to pull.
Andrew
secutanudu is offline   Reply With Quote
Old 07-29-2010, 05:36 PM   #6
Electrician
Rewards Points: 770
If you are useing RW90xlpe you will have to run 1".
Old 07-31-2010, 10:14 AM   #7
#6/3 NMWU copper is good for 65 amps, and since manufacturer do not make 65 amps breaker, the code allow us to go to the next available, which in our case will be 70 amps. So either 60 or 70 amps breaker will do.
It's always cheaper to run a cable, instead of doing PVC conduit run. You will need to bury it 2 feet deep in both cases.
Personally, I do most of my garage and toll shack sub-panels with TECK90 aluminium cable. It's 3 to 4 times cheaper than copper, and the cable is extremely resistant to abuse. In this case you would need #4/3 TECK aluminium cable (good for 65 amps), plus standard connectors to plug it at both ends (do not buy TECK connectors, they are intented for use in wet locations and are expensive, in this case you do not need them).
You cannot buy TECK are your local hardware store, you need to go to the nearest Lumen, Westburne, Nedco, Wesco store...just pick the nearest.
vlatva is offline   Reply With Quote
Old 07-31-2010, 11:26 AM   #8
Rewards Points: 1,016
Is this a Canadian requirement?
Also I suggest to run a amply oversized conduit - makes it easier to pull and can easily accomodate a future change to a larger wire should it be desired.
Old 08-02-2010, 06:21 PM   #9
Electrician
Rewards Points: 770
Where does it say this in the code book, there is the 5% rule but your not with in 5% with this wire.
hi i am wiring my detached garage (in canada) i am puting a 100 amp sub panel in the garage. i was told i need a smaller breaker in the main panel.
No he only wants 60A in the garage but his panel is rated at 100A so in this case he needs to install a smaller(60A) breaker in the main panel.
What type wire to use from transfer switch to outdoor outlet brjl Electrical 32 11-20-2013 09:36 AM
Real Basic Electrical question re: neutral wire hellothere123 Electrical 22 07-21-2009 07:07 PM
Neutral Wire? 4x15mph Electrical 8 11-24-2008 02:00 PM
Should a dryer be 10 gauge wire & range 8/3? twilightcall Electrical 7 07-03-2008 07:29 AM
Gauge Wire and Breaker Discrepancy broken_scout Electrical 26 12-22-2007 11:07 PM