The attached photos show the wire coming in at my home's service entrance. I'm trying to determine what wire size it is....The close up shows 2 AL / 600volt. I presume the AL is aluminum but not sure if this is 2/0 aluminum or #2 aluminum (makes an impact on how difficult a service change is going to be). Unfortunately, there is no writing visible on the hots other than the year - 1975. The breaker on the right is a 100amp breaker.
-thanks
What gauge wire is this?-2013-04-09-07.19.34.jpg   What gauge wire is this?-2013-04-09-07.19.42.jpg   What gauge wire is this?-2013-04-09-07.19.55.jpg
dfelb8 is offline   Reply With Quote
Old 04-10-2013, 03:33 PM   #2
Rewards Points: 734
The wire marking is clear, #2. If it was 2/0 it would say it. #2 is just over 1/4" in diameter, 2/0 would be just about 1/3" in diameter.
#2 AL is appropriate for a 100 amp service.
Yes, it is aluminum.
AandPDan is offline   Reply With Quote
The Following User Says Thank You to AandPDan For This Useful Post:
dfelb8 (04-10-2013)
Old 04-10-2013, 03:45 PM   #3
Thanks, guess I was hoping it was thicker. Is 100amp service the max for this size wire?
Old 04-10-2013, 03:48 PM   #4
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,824
Yes, for a dwelling. Other uses it's less.
The Following User Says Thank You to Speedy Petey For This Useful Post:
dfelb8 (04-10-2013)
Old 04-11-2013, 12:15 AM   #5
" Euro " electrician
frenchelectrican's Avatar
Why ya have to open that box cover below the meter socket and that is typically unfused and that is POCO lateral conductors.
That is good for 100 amp service.
Merci,
Marc
Old 04-11-2013, 07:37 AM   #6
Electrical Contractor
kbsparky's Avatar
That wire is a #2. It is connected to the neutral. Are those others slightly larger? We commonly use a #1 for the hots on a 100 Amp feeder.
In any case, you are most likely limited to a 100 Amp service using this equipment/wires.
-KB
Old 04-12-2013, 02:10 AM   #7
Normally 100 amp service would have a #2 THHN set of wires. #2 is smaller than the #1 copper.
adlermark321 is offline   Reply With Quote
Old 04-12-2013, 08:22 AM   #8
kbsparky's Avatar
The OP is dealing with aluminum conductors here. Copper is a completely different animal.
-KB
Old 04-12-2013, 10:41 AM   #9
jbfan's Avatar
Rewards Points: 144
That looks like the feed from the poco.
The wires under the other cover are the ones you need to be concerned with.
Old 04-12-2013, 01:25 PM   #10
The wire from the breaker panel on the right to the main breaker panel inside the garage is the same wire type and gauge...so, I'm stuck with 100amp scenario until I replace the wire and upgrade the service...
-Thanks
10 Gauge wire with 30amp circuit and Baseboard Heat? RocketManZ Electrical 4 12-17-2011 01:19 PM
What size ground wire should I use for 8 gauge power dxmullin Electrical 1 07-06-2011 03:57 PM
Hot Water Heater Wire Gauge bphilip Electrical 16 09-18-2010 08:23 PM
20A Breaker, 14 gauge wire? joside Electrical 12 08-25-2010 10:41 AM
Neutral Wire? 4x15mph Electrical 8 11-24-2008 02:00 PM