What Feeder Wire Should I Use For 200amp Service @ 220 Feet In 3" Conduit? - Electrical - DIY Chatroom Home Improvement Forum
Old 06-17-2009, 01:03 AM   #1
What feeder wire should I use for 200amp service @ 220 feet in 3" conduit?
I was told 350,350,4/0
Any ideas, thanks
wallstreet is offline   Reply With Quote
Old 06-17-2009, 01:28 AM   #2
This says 4/0 copper
http://www.electrician2.com/calculat...r_initial.html
220/221 is offline   Reply With Quote
Old 06-17-2009, 06:59 AM   #3
Any ideas, thanks
You are on it. 350 for L1 & L2, 4/0 for neutral, #2 for ground .
And XHHW-AL a lot cheaper than copper.
FIA Ranch is offline   Reply With Quote
Old 06-17-2009, 01:51 PM   #4
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,990
If this is for a service these are the service lateral.
All you need for a 200A service at this distance (under 250') is the standard 2/0CU or 4/0AL.
In my area we use URD with 4/0, 4/0, 2/0 AL conductors.
This information should also be available from your POCO.
You DO NOT need a voltage drop calculator for this installation.
Old 06-17-2009, 02:55 PM   #5
Not if you are one of those super smart electricians.
Old 06-17-2009, 03:16 PM   #6
Exactly.
Let me know if you need help with anything.
BTW- if this is a service lateral and not a feeder, then the POCO is usually the one to size the conductors.
250' is usually the limit for "standard" sized laterals.
Tags
200amp , distance , feeder cable , mcm
Remodel - Moving from 200 amp service to 320 amps stevedar Electrical 20 11-29-2009 08:14 PM
This doesnt seem right. JoulesWinfield Electrical 27 07-26-2009 07:40 PM
2x100a sub on service main jambud Electrical 17 03-12-2008 09:31 AM
Sub panel grounding sluggermike Electrical 27 11-11-2007 01:23 AM
Cost to run electric service to home 500 feet away skinnersone Electrical 2 08-26-2007 04:07 PM