What Is Code?? - Electrical - DIY Chatroom Home Improvement Forum
Old 07-16-2008, 09:18 AM   #1
what is code??
i'm installing a condensing unit outside. i bought a fusible 30amp/240vac box as a kill switch. the box is for a/c outside but doesn't say waterproof? can i run 3 different cables to this box? one supply, one to condenser, one to inside evaporator[split system]?? can i double up on load side terminals for condenser & evap?? can i use flex' plastic conduit for all wiring?? can i use regular romex inside these cables or does it have to be water resistant wire?? can i run supply side [unit rated for 2-20amp bkrs.] using 12-2 romex from house panel to inside box and splice to flex cable to go to outside?? do i need to put backer board behind outside box [stucko/brick]?? Thanks for your help.
Jacques is offline   Reply With Quote
Old 07-16-2008, 09:22 AM   #2
P/s
the distances are approx, supply-20'---box to cond unit 4'--box to inside unit 20' Thanks.
Old 07-16-2008, 10:52 AM   #3
Rewards Points: 58
You don't need a fusible disconnect if the condensing unit is protected by the correct breaker in the panel. Use non-fusible.
The box (enclosure) must be rated NEMA 3 R (raintight).
No. The load and line side lugs are rated for one conductor each.
Can I use flex' plastic conduit for all wiring?? can i use regular romex inside these cables or does it have to be water resistant wire?? can i run supply side [unit rated for 2-20amp bkrs.] using 12-2 romex from house panel to inside box and splice to flex cable to go to outside?? do i need to put backer board behind outside box [stucko/brick]?? Thanks for your
help.
You can put Romex in conduit or flex if you want. But that would be a waste of time and money. Just buy UF for the whole run. This cable (UF) cannot be subjected to physical damage. So you can use a small piece of PVC to protect it outside entering and leaving the disconnect.
Mount the disconnect however you wish. I would use concrete screws and mount it directly to the brick. It will look much better.
Old 07-16-2008, 04:18 PM   #4
Electrician
Man, I just enter the back of the disconnet with NM (romex) and just use a little duct seal around the NM connector before pushing the disconnect up against the wall surface...
chris75 is offline   Reply With Quote
Old 07-17-2008, 05:19 AM   #5
Thanks for reply. this is an old twin house, solid 12" stone,brick,plaster, so i have to go outside to run wiring, then back in house to connect. all the disconnect box's i looked at for a/c; only had 2 lugs for load. according to units wiring they want supply to go to inside unit [evap] and then 2 more wires back out to cond' unit. what a mess! i looked at how some neighbors had it done and they were doubled up on load lugs [which you pointed out is not code] how would a real electrican wire this?? Thank You.
Old 07-17-2008, 12:12 PM   #6
Rewards Points: 58
That was the issue. How did he plan to enter the disco. If it's from behind I agree. But the OP never said how. Next thing you know, he's got NM strapped to the bricks outside.
Old 07-17-2008, 12:57 PM   #7
Electrical Contractor
I like going through block with PVC, and a deep 4x4 box mounted on the inside. No questions asked about using NM in a wet/damp location. And it's easy to seal around the PVC pipe.
hpp58 is offline   Reply With Quote
Old 07-17-2008, 04:52 PM   #8
Electrician
Never had a problem, never should be a problem either, but I know locations can have different rules...
Old 07-18-2008, 10:05 AM   #9
But, think about it. Raintight box, Romex connector, they just don't mix.
Old 07-18-2008, 01:46 PM   #10
Electrician
The connector is not outside, its in the wall...
Here is another example, 3R box still equals damp location, so when you install a 3R panel do you buy 3R breakers as well?
How bout this example, pancake box on outside wall for fixture, no difference IMO.
Old 07-18-2008, 02:36 PM   #11
Thumbs down
Not really, A raintight disconnect has little feet where the screw holes are creating an air gap behind the box. When it is mounted on block water can get behind it. I might be splitting hairs, sorry. I work for a pharmacutical co. and I've seen water get into the alot of strange places. I'm a little bit on the crazy side trying to keep water out of electrical equipment. Most of our equipment is washdown rated & stainless steel. I love using Arlington products, they work pretty well for residential work.
Old 07-18-2008, 02:44 PM   #12
Electrician
Your not wrong in your opinion on the subject, I just install some duct seal around the connector and call it good, its just the way I do it...
Old 07-18-2008, 02:52 PM   #13
I've done it both ways, but it's my preferred method.
Stairway landing code question. Bcoleman6 Building & Construction 4 06-26-2008 10:43 AM
Code requirement to replace bathroom window. Rem8 Building & Construction 5 06-16-2008 03:57 PM
underground code tom b Electrical 8 03-23-2008 11:55 AM
Another Bryant 383KVA with code 31 problems rpgIVguru HVAC 1 02-05-2007 02:47 PM
International building code and permits rforsha Building & Construction 4 08-28-2006 07:35 PM