Well Pump Wiring Code Question - Electrical - DIY Chatroom Home Improvement Forum
Old 04-20-2012, 03:44 PM   #1
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,142
Well pump wiring code question
Getting ready to replace my well jet pump with a 240 volt model (currently I use a 120 volt pump. Currently I have a 20 amp, 120 volt circuit that runs from the house to the pump house about 60 feet. I use that circuit for the pump, a light and a receptacle. I want to replace that circuit with a 20 amp MWBC using 12/3 UF cable from the sub panel in my detached barn to the pump house (about 20 feet).
Question: Can I use 1/2" seal-tite to run from the sub panel to a a junction box prior to going underground with the 12/3 UF? The seal-tight run would be about 30". (I have a bunch of seal-tite, connectors and #12 THWN that I bought cheap at a storage unit auction.) The seal-tite would be run in the stud bay and along side the ceiling joist to get from one side of the barn to the other.
Question: Can I use an unfused air conditioning disconnect at the pump house to disconnect the 2 ungrounded conductors of the MWBC.
I can find nothing in the NEC that would bar either of these items, but I am a code novice.
Coastal South Carolina
Old 04-20-2012, 05:32 PM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 240
Yes to both questions
The 12/3 uf will be a tight fit in the 1/2" sealtite.
Old 04-20-2012, 05:37 PM   #3
A "Handy Husband"
rjniles's Avatar
Running #12 THWN in the seal-tite; then switching to the UF for the underground portion.
Old 04-20-2012, 05:42 PM   #4
jbfan's Avatar
Rewards Points: 240
Even better!
Old 04-20-2012, 06:39 PM   #5
Idiot Emeritus
Rewards Points: 1,492
I agree with JB, it'll be compliant.
Just make sure the 12/3 includes a ground.
micromind is offline   Reply With Quote
Old 04-20-2012, 07:17 PM   #6
Ravenworks's Avatar
Are running 240 for just the pump, and using the old wire to run the 120?
I don't think you can mix the two
They do make a disco with an outlet already installed,maybe you can get your 110 from the outlet?
A Sparky will be along soon to answer.
Ravenworks is offline   Reply With Quote
Old 04-20-2012, 07:28 PM   #7
joed's Avatar
Rewards Points: 12,002
You are going to need a sub panel in the shed to create the 240 and 120 volt circuits.
Old 04-20-2012, 07:59 PM   #8
Electrician
Rewards Points: 150
Joed suggests a sub panel at the pump house. This would be wise for future uses, but much more complicated. The code requires a sub panel is fed by a minimum of 30 amps (10 wire copper), separates the neutral and ground busses, has a grounding electrode (ground rod, well pump case or other) and more. If you stick to a MWBC, get a big waterproof j box, like 10" x 10" and all waterproof couplings for the penetrations.
Glennsparky is offline   Reply With Quote
Old 04-20-2012, 08:10 PM   #9
Electrician
Rewards Points: 150
I reread your second question. You can do all your connections and penetrations in the AC disconnect if you don't exceed box fill and don't put multiple wires in one lug.
Old 04-20-2012, 09:40 PM   #10
A "Handy Husband"
rjniles's Avatar
The existing 20 amp circuit will be removed. I will use the 20 amp MWBC for both the pump; light and GFCI receptacle. I believe there is an exception in the MWBC code section that allows it. I will come off the disconnect with a single 12/3 and break out the 240 and 120 in a junction box.
Edit-- 210.4(C) Exception #2 and requires a 2 pole common trip breaker
Old 04-20-2012, 09:44 PM   #11
kbsparky's Avatar
Provided you use an internal common-trip double pole breaker, this is allowed.
-KB
The Following User Says Thank You to kbsparky For This Useful Post:
rjniles (04-21-2012)
Old 04-21-2012, 06:39 AM   #12
A "Handy Husband"
rjniles's Avatar
Reading another thread on wiring for an AC unit gave ma an idea:
I will use this for the disconnect and wire off the load side of the GFCI for my lights (eliminates the need for an additional junction box.) I will still need the 2 pole breaker in the originating sub panel
Old 04-21-2012, 11:54 AM   #13
Ravenworks's Avatar
That is what I posting about.
See post #6
The Following User Says Thank You to Ravenworks For This Useful Post:
Craftsman Pressure Washer 580.761800 pump question SteveLake Tools 0 06-22-2011 10:51 PM
Help with Heat Pump System Wiring AlanScott HVAC 11 10-10-2010 01:19 PM
Pump for a furnace question! PLEASE HELP! . VERY COLD LOL dvandam HVAC 9 12-12-2009 08:48 AM
Basement wiring question kupalino Electrical 8 11-14-2009 10:25 AM
Well pump wiring, the correct guage? lennyjay Electrical 3 08-18-2009 01:53 PM