Old 04-25-2012, 01:07 PM   #1
Welder receptacle Location
Is there any reason I can't mount a 50 amp receptacle for a welder a few inches below the panel to save on the cost of the wire? Is THHN or 6/3 nm preferred?
MisterSteve is offline   Reply With Quote
Old 04-25-2012, 01:46 PM   #2
only catch may be dedicated equipment space. the area below the panel is "dedicated to the electrical installation". sort of a gray area if utilization equipment receptacles can be within this area.
itsnotrequired is offline   Reply With Quote
Old 04-25-2012, 02:30 PM   #3
Code05's Avatar
Not IMO, it is part of the associated equipment to the electrical installation. How would this be different from a conviennce receptacle?
(a) Dedicated Electrical Space. The space equal to the
width and depth of the equipment and extending from the
floor to a height of 1.8 m (6 ft) above the equipment or to
the structural ceiling, whichever is lower, shall be dedicated
to the electrical installation. No piping, ducts, leak protection
apparatus, or other equipment foreign to the electrical
installation shall be located in this zone.
Code05 is offline   Reply With Quote
Old 04-25-2012, 03:10 PM   #4
like i said, sort of a gray area. most of the time it isn't an issue, especially for smaller things. it relates to 'dedicated to the electrical installation' interpretation. an example would be a transformer serving a panel board, with the transformer only a foot or so above the panel. as long as that transformer placement doesn't violate the working space height, is it acceptable? i've seen inspectors reject it. electricians absolutely hate it. i like to see only conduit in the 6 foot area above a panelboard but that's just me. but for something like a top entry panelboard with a receptacle underneath, not a problem.
Old 04-25-2012, 03:15 PM   #5
Licensed Electrician
k_buz's Avatar
As long as the welder isn't bolted down, it would be acceptable.
Old 04-25-2012, 03:24 PM   #6
Code05's Avatar
transformer is legal as long as it does not violate working space requirements.
Old 04-25-2012, 03:31 PM   #7
yes, it is legal but ugly.
here's one for you: say that transformer didn't serve the panel below it but instead served some other panel. i believe technically it is still legal but in my opinion, this is getting into an area where it is 'abusing' the intent of the dedicated equipment space requirement.
Old 04-25-2012, 03:41 PM   #8
Code05's Avatar
I agree, but I could block the whole space with troughs and be legal.
Old 04-26-2012, 11:56 AM   #9
So, would it be acceptable to have a 4" square metal box on a 50 amp receptacle about 4" below the panel within the same stud bay with #6 THHN in 3/4"emt.
Outside receptacle location WillK Electrical 2 09-11-2010 09:39 AM
Using a multimeter to test a 50 amp receptacle WendyS Electrical 12 01-22-2010 09:10 AM
changing 3 prong receptacle to 4 prong WendyS Electrical 12 01-17-2010 09:59 PM
Wiring timer from receptacle intotao Electrical 7 01-21-2009 09:57 AM
Split Receptacle on 3-Way Circuit NPS Electrical 6 11-03-2005 10:28 AM