-   -   water pump breaker humming and tripping (http://www.diychatroom.com/f18/water-pump-breaker-humming-tripping-116864/)
hammer60 09-10-2011 06:50 PM
my water pump breaker is tripping---when i reset it, it hums and then trips again------i pulled the disconnect for the pump and reset the breaker and it didn't trip-----just want to make sure if i should be looking at more of an issue with the water pump---thanks
Code05 09-10-2011 07:00 PM
Water pump or the wire from disconnect to water pump. Assuming breaker is good.
SD515 09-10-2011 07:04 PM
You pulled the disconnect and the breaker holds when reset, that tells you the problem is in the disco, the wiring from it to the pump, or most likely in the pump itself.
Code05 09-10-2011 07:08 PM
Or a bad breaker, no?
SD515 09-10-2011 07:27 PM
You beat me to it :)
Possible. Yes.
SD515 09-10-2011 07:34 PM
Maybe it's had enough alcohol to drink?
hammer60 09-10-2011 07:47 PM
thanks
i'll check the pump
dmxtothemax 09-10-2011 08:05 PM
It could be either the pump, or the breaker !
But it would be cheaper to replace the breaker first !
If a new breaker doent fix it ,
then you have a problem with your pump.
I assume you have checked all the simple things first,
like loose / dirty / faulty connecttions / damaged cord
frenchelectrican 09-11-2011 01:57 AM
Which type of water pump you have there?
Sub pump or shallow well pump ?
Once you give us little more info we can assit you on this real quick.
Merci,
Marc
AllanJ 09-11-2011 08:39 AM
Things to check:
Pressure tank waterlogged.
Pump clogged or jammed.
Pipes clogged.