Water Heater Bonding - Electrical - DIY Chatroom Home Improvement Forum
Old 01-23-2013, 10:16 PM   #1
Water heater bonding
when grounding a hot water heater is it best to ground both the hot outlet and cold inlet? Also, what gauge copper wire is best to use?
mikem201 is offline   Reply With Quote
Old 01-24-2013, 12:29 AM   #2
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
Are you talking about this which is bonding not grounding
Old 01-24-2013, 07:26 AM   #3
Licensed electrician
Rewards Points: 1,502
What size is the service?
Old 01-24-2013, 07:45 AM   #4
Rewards Points: 1,500
Bonding at the water heater consists of the following:
1. A bonding jumper, pictured above, between the water heater inlet and outlet. It would be #6 copper for electric services up to 100 amps, #4 for services of 100 to 150 amps, I don't have the table handy for larger services. If either or both of these are plastic then the bonding jumper(s) go from each metal section of the hot water plumbing downstream (upstairs, etc.) to grounding electrode conductors or bonded metal cold water pipe.
2. One of:
2a. For water heaters that use electricity, the properly connected equipment grounding conductor in the electrical feed.
2b. For gas water heaters that don't use electricity, a bonding jumper from the gas piping (anywhere along it) to a grounding electrode conductor or grounding electrode.
Plumbing may not be part of the equipment grounding path from an electrical load (light, appliance, receptacle, etc.) to the panel. One of the reasons is that the chance exists that at a later date a section of plastic pipe may be substituted for metal pipe and installation of a bonding jumper across the plastic section neglected.
Old 01-24-2013, 08:22 AM   #5
service is 100amps. What is difference between bonding and grounding? FYI my hot water heater is gas.
Old 01-24-2013, 09:52 AM   #6
Bonding -- Interconnecting two metal items using an essentially resistance free electrical connection. If A is bonded to B and B is bonded to C then A is bonded to C. Electrical codes include additional rules that imply how many amperes must be able pass over the interconnection. For example an adequate bond might be a #20 gauge wire between a component and the chassis inside a TV set but might need to be a #4 gauge wire between an electrical panel and a water pipe.
Grounding -- (1) Connecting (bonding) to a properly installed ground base (grounding electrical system) of an electrical system. The GES consists of the ground rods, main water pipe if metal exiting the house underground, neutral/ground bus bar in the panel with the first main disconnect, and fat (typically #6 copper) wires (grounding electrode conductors) connecting these items. (2) Providing contact with the ground (earth, soil) using means such as ground rods or the reinforcing bar inside a buried concrete slab, sometimes metal plates.
Old 01-24-2013, 09:53 AM   #7
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
Bonding eliminates any difference of potential. Grounding means connected to the grounded service conductor and grounding electrode system in the building.
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
The Following User Says Thank You to electures For This Useful Post:
danpik (01-24-2013)
water heater drip kdange1 Plumbing 6 10-29-2014 05:26 PM
How to properly drain and flush a hot water heater? speedster1 Plumbing 9 04-17-2012 09:55 PM
no water at sink after water heater removal rebelbull Plumbing 2 07-19-2011 12:37 AM
A blocked water line causing water to loose heat? Snav Plumbing 6 05-07-2010 02:18 PM
Water heater pressure relief valve confusion Flt_Simulation Plumbing 4 07-11-2009 10:02 AM