Want To Upgrade Home From 200A To 400A Service - Electrical - Page 3 - DIY Chatroom Home Improvement Forum
Old 02-23-2014, 03:50 PM   #31
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Originally Posted by brric View Post
A 20 amp circuit should be limited to 16 amps for a continuos load (3hours or more ).
IMO, the only items that should be considered continuous in a residence is Electric heat, and electric water heater...
Old 02-23-2014, 05:46 PM   #32
Master Electrician
Rewards Points: 3,870
You are entitled to your opinion.
brric is offline   Reply With Quote
Old 02-23-2014, 06:29 PM   #33
Originally Posted by Daniel Holzman View Post
You see the breaker at the top of the panel labeled 200A? That is a 200A, 240 volt breaker, so you have a 200A service, with a total capacity of 200A * 240V = 48,000 watts = 48 kilowatts (kw). In order to figure out how much spare capacity you really have, you need to do a load calculation on all of the devices and lights attached to your panel. But your electrician will be pleased to do this for you, as part of any required upgrade in service. Anyone who can afford 21KW worth of computers can surely afford an electrician to do the necessary work.
you can tell that's a 240v breaker from experience, or there's some indication?
well, this is what I was looking for. I highly doubt the rest of the panel comes anywhere near the remaining 27 KW capacity, but I may have my electrician take a look anyway.
starfighter is offline   Reply With Quote
Old 02-23-2014, 07:03 PM   #34
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,956
It's funny how his opinion and the code coincide.
The Following 4 Users Say Thank You to Speedy Petey For This Useful Post:
brric (02-24-2014), jbfan (02-24-2014), Philly Master (02-25-2014), stickboy1375 (02-24-2014)
Old 02-23-2014, 07:26 PM   #35
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
Just about every home in the US is fed with 120/240V. You do have other 240V circuits fed from your panel as well.
Old 02-24-2014, 08:41 AM   #36
As long as the circuit is at 80% capacity, it shouldn't matter if it is run continuously or not
Old 02-24-2014, 09:21 AM   #37
Master Electrician
[QUOTE=starfighter;1312153]As long as the circuit is at 80% capacity, it shouldn't matter if it is run continuously or not[/
Deleted
Old 02-24-2014, 02:46 PM   #38
Rewards Points: 3,396
For what ever it's worth..........
yes 3 hrs or more is continuous in my book also.................
BUT - I have heard stickboys "opinion" in "many" places being the same in residential.. NJ 36 hr. continuing education courses..... electrical forums, not DIY forums........... For what it's worth...
as you were...
ritelec is offline   Reply With Quote
Old 02-24-2014, 03:07 PM   #39
Where is this 80% capacity rule you speak of?
The Following User Says Thank You to Speedy Petey For This Useful Post:
Old 02-24-2014, 03:54 PM   #40
E2 Electrician
as you were...
If you read the definition, there really are only two items that fall into that category in residential...
Old 02-24-2014, 08:43 PM   #41
You left out the most important word......"EXPECTED".
Old 02-27-2014, 10:48 PM   #42
Electricians that I have talked to have said circuits shouldn't be continuously run at more than 80%. I don't know why they would say that, I presumed to keep wiring from overheating or something, but I am no electrician (as this thread has shown). I would like to know the reasoning behind this, or if it is incorrect - can circuits be run at full capacity 24/7, assuming adequate wiring?
Old 02-28-2014, 05:46 AM   #43
True, for continuous loads there is an 80% limitation.
Thing is, you need to look at the definition of "continuous load" in the NEC. Very little in a home is or would be considered a continuous load.
The Following 2 Users Say Thank You to Speedy Petey For This Useful Post:
jbfan (02-28-2014), stickboy1375 (02-28-2014)
Old 02-28-2014, 02:43 PM   #44
I have computer equipment that is running 24/7, and I am trying to make sure I have proper circuit loading in place.
Old 02-28-2014, 03:05 PM   #45
True enough, but even that is not running at full load full time. Just because a power supply is rated at 450 watts for instance does not mean it draws 450w all the time it is on.
I assume you have a UPS with a digital display. Put the display on load and watch the watts fluctuate.
Tags
amps , electrical , home , service , upgrade
Questions regarding 100amp service and panel upgrade asledge Electrical 38 12-12-2012 11:57 PM
400A underground Main service intelspec Electrical 7 02-22-2012 01:22 AM
200A upgrade and move, backfeeding permitted? WillK Electrical 3 05-30-2011 08:00 PM
Who owns a Home Warranty Service? oggy bleacher Off Topic 14 05-18-2011 02:24 AM
Juggling power during service upgrade. WillK Electrical 2 05-04-2011 05:40 AM