-   -   Voltage Problem (http://www.diychatroom.com/f18/voltage-problem-82092/)
H. Bruce 09-22-2010 07:49 PM
Voltage Problem
This evening I decided to install a new light fixture in my backporch and found a voltage problem as described below.
1. Voltage between hot wire and ground, breaker on and light switch off
1 volt.
2. Voltage between hot wire and neutral, breaker on and light switch off
1 volt
3. Voltage between hot wire and neutral, breaker on and light switch on
120 volts.
Why is there 1 volt remaining on the first two when in fact there shouldn't be any? Any help would greatly be appreciated, thanks
nap 09-22-2010 08:17 PM
are you using a digital multimeter (DMM)? If so, you likely have "phantom voltage". It isn't really phantom but an induced voltage with such a low current capacity it is basically disregarded.
frenchelectrican 09-22-2010 09:25 PM
Nap have the point if you have ditgal Voltmeter they can pick up ghost voltage by induction of other conductors.
If you have a indentscent bulb hooked up you will read zero as you highlight first two parts.
Merci.
Marc
H. Bruce 09-23-2010 08:41 PM
I do not have a digital multimeter, I'm using one with a meter on it. Thanks to both of you for answering. Will I just go a head and install
the new light fixture, but what about that 1 volt? Will it not cause a problem?
frenchelectrican 09-23-2010 08:43 PM
naw I don't think so as long you hook them up in correct way.
Some of the voltmeter can be supersenstive that why sometime can get false reading.
Merci.
Marc
H. Bruce 09-24-2010 12:14 PM
Thanks "frenchelectrican" and "nap" for the information and help I certainly appreciated it. I always thought for induction to be involved the wire had to be in the form of a coil such as a transformer.
I scrolled down the page and see a similar posting or thread ,"small voltage on circuit with breaker off ", by jasonmechler (24 aug 09).
Thanks to all and good afternoon from Eastern Canada.
Bruce