Voltage On Line That Is Turned Off? - Electrical - DIY Chatroom Home Improvement Forum
Old 03-22-2013, 09:48 PM   #1
Rewards Points: 640
Voltage on line that is turned off?
I've been having some odd electrical issues tonight... have a hum coming from the service panel that starts quiet gets louder to a point then goes back down... kinda like a sine wave pattern but it takes about 10 seconds to cycle...
so I checked new lines that were ran for the basement... on the outlets I don't get zero volts..
Ground to neutral 0.0v
Hot to ground 0.255v
Hot to neutral 0.256v
this breaker is off... I expected 0.0 for all connections, but all the lines in the house are running in a bundle basically parallel for 50 ft to get to this point... could this voltage be coming from induction? Or is it normal to get a low voltage from hot to neutral or ground when a breaker is thrown off?
When the breaker is on, I get 125v
House Information: Build 1996, 1500 sq ft basement, 1500 sq ft 1st floor, 800 sq ft 2nd floor, 560 sq ft unfinished attic space on 2nd floor. Insulation: Attic blown fiberglass, walls R-19, Basement R-19. HVAC: Trane xc95m fully modulating furnace, single zone, Trane XL20i commiunicating AC unit, TCONT900 Communicating thermostat.
BlueBSH is offline   Reply With Quote
Old 03-22-2013, 10:01 PM   #2
Rewards Points: 506
The voltage could be Phantom Voltage. The DMMs will read that.
The humming could be a loose connection in the panel, neutral perhaps, or maybe a breaker isn't seated well?
Old 03-22-2013, 10:15 PM   #3
Almost certainly it is phantom voltage, or induced voltage, which would come from all the conductors running parallel to each other. The numbers you measured are extremely low (about 1/4 of a volt, a size AA battery is 1.5 volts). As Sirsparksalot said, the digital meters are extremely sensitive, and will pick up induced voltage in the wires. The low voltage reading sounds normal for this situation. As for the buzzing, I have experienced some breakers that are well seated and just make noise (internally), or it could be a loose connection. Are these the correct breakers for the panel? (just because they fit in the panel doesn't mean they were designed to be used in the panel) If you are comfortable with opening the panel box, I would pull the breakers out, and re-seat them, that perhaps could take care of the buzzing.
dan1554 is offline   Reply With Quote
Old 03-22-2013, 11:03 PM   #4
Rewards Points: 640
the humming seems to be coming from the main breaker... yesterday it wasn't humming... the odd thing is how it starts quiet then builds then goes back down then repeats....
made sure all the breakers are seated fully, and they seem to be, all wires are in tight... all the breaker models match what the panel lists as acceptable breakers for this panel (its a GE powermark gold load center 200amp) every breaker is one of those half height breakers
Old 03-22-2013, 11:10 PM   #5
It sounds like you have covered all the bases... with all of today's electronic equipment, that could possibly account for the humming variation. Does the main breaker feel warm? It should be room temperature unless under very heavy load, or if there's a loose connection. I have an infrared temperature gun that has been invaluable for troubleshooting of this nature, but without one, it should not feel warm to the touch. From time to time I have heard buzzing noises from my panel, but that was several years ago and no problems have shown up, although I was never able to track down the cause of the noise. Haven't noticed it in several years. As long as all the connections are tight and none of the breakers are warm (or hot) to the touch, I don't think you have anything to worry about.
Old 03-22-2013, 11:19 PM   #6
Rewards Points: 6,652
Phantom voltage due to cheap meter you are using. One of these http://www.lowes.com/Search=digital+...tal+multimeter will work better than what you are using. Personally, I prefer the Fluke, but the Ideal will work fine. Without going out and getting a new DMM/DVM, you need to place a load like a 60w incandescent lightbulb on the line in series between the hot & the Red lead, then check your readings again.
Old 03-23-2013, 07:25 AM   #7
Rewards Points: 640
http://www.testequipmentdepot.com/fl...FYid4AodXBMACA
that's the meter I am using, I sure hope that doesn't qualify as cheap
Old 03-23-2013, 03:17 PM   #8
Nope, one of the better. Just picking up inductance voltage from a line that is along the same run as that one, or in the same junction box.
Your fluke should not be picking up Phantom voltage with that model. What voltage range did you have it set for, when you were testing?
Old 03-24-2013, 10:25 AM   #9
Rewards Points: 640
Was set up for auto ranging at the time, if I put it into a lower range manually I get the same results...
I just tried something different too... I put one lead on a ground that is grounded and the other lead on the other ground line that right now isn't connected and got 26.543v
Starting to wonder if my meter is going wacky
Old 03-24-2013, 11:46 AM   #10
You can send it back to fluke to have it calibrated. What happens if you place a small candelabra in a base with the two leads, so you can use it to place some resistance on the line, then you should see the phantom voltage go away. You could also use a 16 Ohm resistor with some alligator leads, in place of a light bulb.
Old 03-24-2013, 11:55 AM   #11
Electrical Contractor
jbfan's Avatar
Rewards Points: 144
Change the battery
First you were reading millivolts, and not reading volts?.
jbfan is online now   Reply With Quote
Old 03-24-2013, 12:50 PM   #12
Rewards Points: 640
Originally Posted by jbfan View Post
Change the battery
yes it says V not mV
Old 03-24-2013, 12:51 PM   #13
Rewards Points: 640
if I put resistance in series I get 0.124v
Old 03-24-2013, 01:39 PM   #14
Then I would not worry about it. I usually just place my meter in 200vAC to measure, not Auto-Ranging.
Voltage sag or VD. Where do they draw the line in the sand? viper Electrical 43 05-18-2011 03:56 PM
Flickering lights on circuit with low voltage and line voltage bulbs davidwiesel Electrical 4 04-18-2011 09:54 AM
Line Voltage Thermostat Wiring bswigart Electrical 10 11-24-2009 08:10 PM
programmable line voltage therm for fan heat nykije HVAC 1 11-18-2009 10:51 PM
wiring a line voltage programmable thermostat cedar HVAC 0 10-24-2009 11:30 PM