-   -   voltage drop (http://www.diychatroom.com/f18/voltage-drop-16951/)
HandyAl 02-11-2008 05:10 PM
voltage drop
We've experincing voltage drop on some of our lights and outlets since after a heavy rain last week. I need some advice on who to call.
I check the feed going into the distribution panel. One side was 143 volts and the other 98 volts. Should I called th power company or the an electrician?
chris75 02-11-2008 05:13 PM
You have a neutral problem call either an electrician or your poco ASAP!!!! Either or but HURRY!!!
goose134 02-11-2008 10:10 PM
Al, I agree 110% with Chris. Neutral. Bad. Electrician first, POCO second.
chris75 02-11-2008 10:13 PM
His computer is probably cooked by now... :(
HandyAl 02-12-2008 01:47 PM
Voltage drop UPDATE
Power company came out today and found a bad neutral in the drop coming from transformer to the house. They're got a temporary copper line running on the ground until they can get a work order to bury a new drop.
chris75 02-12-2008 03:38 PM
Dont forget, most POCO's are liable for any damage to your house so make records of the events if anything gets damaged...
goose134 02-12-2008 08:03 PM
Good point Chris. Glad this was taken care of. These types of things get ghastly and most people don't catch them until it is too late.
HandyAl 02-13-2008 05:50 PM
The only thig I can see that went bad is one CFL bulb.