Bought a Kill-a-Watt to determine if I should replace my fridge now or later. While it works, I noticed it has a readout for voltage. When the fridge motor is off, it reads 119.9-120.1 volts. Pretty spot on.
When the compressor kicks on, and the microwave is on full power, voltage droops a bit... down to about 113 with a heavy load from other appliances on.
How much droop should one see in the voltage before they get worried?
Thadius856 is offline   Reply With Quote
Old 08-03-2011, 06:21 AM   #2
Rewards Points: 1,448
A voltage drop at the refrigerator receptace of that amount means that the drop is in the wires, not in the 'fridge. It may be normal if the kitchen is some distance from the breaker panel, or you may need to tighten up connecctions and also redo the connections at each outlet box to screw the wires onto each receptacle unit instead of relying on the push-in-and-stick (aka backstab) holes in the backs of the receptacles. (Holes where a screw on the side tightens up the wire are just as reliable as screw on connections)
Now if the voltage in the entire panel drops that 6 volts then taking the time to tighten up individual circuits can be procrastinated upon for now. You can get an excellent idea of drop in the at the entire panel by measuring between a dfiferent breaker screw from the 'fridge circuit and the neutral bus bar.
The Following User Says Thank You to AllanJ For This Useful Post:
rflenniken (08-03-2011)
Old 08-03-2011, 09:03 AM   #3
Is the fridge and microwave on the same circuit? If so, you may want to split them up to their own circuit if it's that bothersome for you. May have been to code when it was wired originally.
CheapCharlie is offline   Reply With Quote
Old 08-03-2011, 12:59 PM   #4
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
5% voltage drop is acceptable for branch circuits.
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
Old 08-03-2011, 01:53 PM   #5
Is it really in the NEC? Could very well be. Here in Canada it's 3% for branch circuits (from main panel).
Old 08-03-2011, 02:01 PM   #6
electures's Avatar
It is a FPN (Fine Print Note).
3% Feeders
5% Branch circuits
5% Feeder/branch circuit combined.
Old 08-03-2011, 02:04 PM   #7
3% Feeders
5% Branch circuits
Good to know
From the CEC:
3% Feeder or branch circuit
5% combined
The Following User Says Thank You to CheapCharlie For This Useful Post:
electures (08-03-2011)
Old 08-04-2011, 12:31 AM   #8
Thadius856's Avatar
Rewards Points: 504
It's not bothersome to me. It's a fairly old fridge and large microwave, plus lights and other recepts in use when getting that reading.
While it's a late 50s home, previous HO seems to have replaced half the recepts and backstabbed them all without pigtails, so I'm switching them as I go, and retrofitting grounds to each box as work allows and cleaning up the wire mess.
While on the topic, I'm finding that at least half of the Cooper brand decora rockers installed have developed a "pop" and I'm replacing them as I find them. Is this a result of the backstabs or a maybe a bad lot?
voltage on earth wire Spikeyboy Electrical 13 10-15-2010 12:03 PM
Above normal Voltage coming from city lines P Marage Electrical 26 10-13-2010 09:01 PM
Voltage in Metal Roof and Gutters TITAN2390 Electrical 4 10-07-2010 08:44 PM
New recessed lighting: Line Voltage vs. low voltage hyunelan2 Electrical 0 10-12-2009 01:25 PM
Low voltage box question WShawn Electrical 7 08-19-2008 07:22 AM