Voltage Difference Between Legs - Electrical - DIY Chatroom Home Improvement Forum
Old 12-16-2010, 12:07 AM   #1
voltage difference between legs
Power company came out said there is an internal (inside the house) neutral problem. Anytime a load is placed on the service a difference between the two legs is seen. The bigger the load the larger the difference. What could cause this
john68112 is offline   Reply With Quote
Old 12-16-2010, 12:51 AM   #2
nap
You talking to me?
nap's Avatar
Rewards Points: 6,290
a neutral problem
where specifically are you measuring the voltages?
The Following User Says Thank You to nap For This Useful Post:
john68112 (12-16-2010)
Old 12-16-2010, 08:20 AM   #3
joed's Avatar
Rewards Points: 13,322
Power company is correct. Could be in the meter base. Did the POCO check in the meter? That is their territory. If they did then it is likely the main neutral connection inside your panel.
The Following User Says Thank You to joed For This Useful Post:
Old 12-16-2010, 09:50 PM   #4
Originally Posted by nap View Post
a neutral problem
Between neutral and the breaker or the feed lines doesnt matter. Someone I talked to said it could be someone has connected a neutral from one leg to the neutral of the other leg somewhere in the house.
Old 12-16-2010, 09:53 PM   #5
I replaced weather head, wires, meter socket, fuse panel(installed breaker box)and installed a ground rod.
Old 12-16-2010, 10:06 PM   #6
Neutral is neutral! It wouldn't matter if they did so.
It means that there's a poorly made neutral connection somewhere.
So current to the load is returning back to the transformer via the other power leg, rather than the neutral.
If this occurs a symptom would be lights being dimmer or brighter than others.
It would be bad for motors in refrigerators, freezers and furnaces.
On service panels that have fuses in the main disconnect, a fault like this is easy to find. However, a breaker panel can be tricky.
A clamp on ammeter would be the best tool for this job.
The Following User Says Thank You to Wildie For This Useful Post:
Old 12-16-2010, 10:21 PM   #7
how would it return through the other leg when it is not a 220 circuit. The only 220circuit is a dryer nothing else. You are right about motors furnace motor had to be replaced and is was one year old.
Old 12-16-2010, 10:35 PM   #8
nap
You talking to me?
nap's Avatar
if you take 2 120 volt circuits that share a neutral and remove the neutral, you now have a 240 volt circuit but the devices are seriesed on that circuit and due to the difference in impedance of the various devices, you will get varied voltage readings.
john68112 (12-17-2010)
Old 12-16-2010, 10:39 PM   #9
joed's Avatar
Did this fix the problem? I hope so, because there is nothing left to change.
Old 12-16-2010, 10:42 PM   #10
Without a clean neutral your home becomes a complex series parallel circuit. Depending where the neutral problem is, will affect the over-all picture.
If you have air conditioning, you will have 220. Electric dryer will have 220. An electric stove as well. In fact your prob. could even be in a stove.
Even if you had none of these, a loose connection in the panel or in the meter base could be the culprit also.
Old 12-16-2010, 11:19 PM   #11
Replaced everything new from power company connection (meter socket, panel, dryer wire and plug, ran new wire to range and right now the house has has a gas stove so its not used also installed ground rod). I moved one of the breakers to another position in the panel and it seems to have took some of the variation in voltage away. Someone had added a plug in kitchen, put aplug in the bathroom and took some older 2 prong outlets and replaced with 3 prong at some point in the past a lady told me it was a live in boyfriend of hers that took it upon himself to HELP her out... The furnace gave out later that day when I wiggled the wire feeding it it started up so I ran a new wire to it. One day later it was out again everything was good(meaning transformer and thermostat turned on gas valve) except blower motor would not start I replaced the motor it was fine.
Old 12-16-2010, 11:23 PM   #12
No it is still the same I thought the same thing replace it all it would be fixed..
Old 12-16-2010, 11:52 PM   #13
Electrical Contractor
kbsparky's Avatar
maybe its time you called in a real electrician. Probably will be cheaper than replacing everything in sight, since he will fix the real problem, instead of shooting in the dark.
-KB
Old 12-17-2010, 12:17 AM   #14
it all needed to be updated it was 1940s technology but thanks for your input
Old 12-17-2010, 06:13 AM   #15
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,972
You are just throwing work at this hoping that it will get better.
CALL AN ELECTRICIAN to find this neutral problem. Unless you are skilled at electrical troubleshooting you are only going to perpetuate the problem, and possibly make it worse.
You say you moved a breaker? Are you sure it was not part of a multi-wire (shared neutral) circuit? If it was you could have possibly fixed the voltage problem, but made just as big of a problem by overloading the neutral of that circuit.
The Following User Says Thank You to Speedy Petey For This Useful Post:
voltage on earth wire Spikeyboy Electrical 13 10-15-2010 11:03 AM
no voltage between legs of a 230v circuit brandonmcginnis Electrical 15 02-14-2010 11:22 PM
Voltage Difference between legs mimitche Electrical 13 05-02-2009 09:37 AM
Low voltage box question WShawn Electrical 7 08-19-2008 06:22 AM
2 - 900w tansformers on a 15A circuit? tonyBagadonuts Electrical 19 07-20-2008 07:15 PM