Using EMT to protect NM cable
Using EMT to protect NM cable running along side furring strips which I will not be able to easily maintain the 1 1/4" cable clearance. I have almost completed installing 1/2" EMT on the walls to the 4x4 boxes. A few questions that have popped in mind.
Obviously ream the EMT, but should I use Insulating bushings on the end of the EMT where it transitions back to NM cable or should I use the NM to EMT adaptor? I've heard of it done either way on older forums, just wondering if either is more desireable than the other by today's standards.
Also, I'm looking for information on how close to the end of the EMT must the pipe be secured. I couldn't find it in the code book. Is there a requirement as to how close to within the end of a piece of EMT used to protect a NM cable has to be secured? I know it's for sure spelled out if you use it as an entire system from point A to Z, but no mention that I'm seeing. I haven't seen anything in the 334.15, and I looked in the EMT section "358" and didn't see anything in reference to using it for protection. Quite possible I'm just looking right past it.
Thanks a bunch for your help guys. Here is a pic to give you an idea of what I'm up to.
kossuth is offline   Reply With Quote
Old 03-26-2012, 09:57 PM   #2
Missouri Bound's Avatar
It's a good idea to protect the wiring. As a protective device rather than part of the electrical circuit you have a bit of leeway in fastening the conduit. But from what it looks like you know a bit about conduit bending and installation. Any reason you just don't do it all in conduit? And if you look around a bit you will find proper conduit techniques and I am sure that information will appear here from one of the other members. Good luck
Do you want it your way or the right way?
Old 03-26-2012, 10:01 PM   #3
Rewards Points: 27
Thanks, I used to do quite a bit of it when I was in the military many many years ago, so it's almost second nature (I hated doing it though LOL). I probiably could run conduit "all the way", but there are quite a few circuits that are going into just regular "timber" walls so for the sake of simplicity as far as wire running I figured it would be best to transition it.
Old 03-26-2012, 10:14 PM   #4
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
Put a EMT coupling on the end of the stub ups, run the romex thru, and staple it within 1' of it entering the pipe...that's what I normally do. But there is nothing wrong with using romex to EMT connectors either.
Old 03-27-2012, 06:34 AM   #5
Rewards Points: 2,516
"Maximum support interval for EMT is 10 ft
In addition, must be securely fastened within 3 ft of each conduit termination(outlet box, junction box, device box, cabinet, conduit body, etc.)
Unbroken lengths of EMT can be fastened within 5 ft where structural members do not readily permit fastening within 3 ft."
All that being quoted, I think you are looking good where you have the EMT terminating. You do have the single hole straps there. Just get some EMT to NM connectors and finish up.
Nice bends on the EMT.
hammerlane is offline   Reply With Quote
Old 03-27-2012, 07:56 AM   #6
Electrical Contractor
kbsparky's Avatar
Or, a simple plastic bushing pressed into the open end of the pipe:
-KB
The Following User Says Thank You to kbsparky For This Useful Post:
Hardway (03-27-2012)
Old 03-27-2012, 08:05 AM   #7
big box stores have these?
Hardway is offline   Reply With Quote
Old 03-27-2012, 11:47 AM   #8
If you are referring to the EMT to NM coupling I believe so.
Is Tray Cable acceptable for Residential use? MisterSteve Electrical 43 02-21-2012 12:35 AM
Need help sizing Generator cable dgajr Electrical 2 07-20-2010 12:07 AM
Evaluating a kinked cable dave11 Electrical 5 05-09-2010 10:20 AM
Underground service entrance cable requirements. kgt55 Electrical 9 06-22-2009 06:55 AM
Running Sky+ cable bookersbeauty Electrical 1 04-09-2009 07:12 PM