Using Bigger (legacy) Wire For Smaller Amperage - Electrical - DIY Chatroom Home Improvement Forum
Old 05-14-2011, 03:06 PM   #1
Rewards Points: 1,062
Question
using bigger (legacy) wire for smaller amperage
i replaced my electric dryer for a gas one and now i have a vacant 30A circuit with 10/3 gauge cable going through the house.
at the same time, i am putting up a powder room where the old dryer used to be and there will be a bathroom above as well.
i wanted to have a 20A circuit going to the powder room and the bathroom. i was wondering whether it is OK for me to reuse the legacy 10/3 cable if i do replace the 30 for a 20A breaker at the panel. i would do it just to the powder room and then i would, of course, go with a 12 gauge... just so i don't have to pull the old cable out and replace it with the adequate 12 gauge. i'm guessing smaller amperage should be OK going through fatter wire. obviously, i there would be an unused wire in the cable in this scenario but i don't care.
Old 05-14-2011, 04:56 PM   #2
Electrician
SD515's Avatar
Rewards Points: 504
The short answer is yes. The ampacities listed in the code are the minimum. You can always use a larger wire than necessary as long as the terminals will accept said gauge.
Kyle
The Following User Says Thank You to SD515 For This Useful Post:
amakarevic (05-14-2011)
Old 05-14-2011, 04:59 PM   #3
Smile
sweeeeeeeet !!!! thanks ... that saves me a lot of time and $$
Old 05-14-2011, 07:19 PM   #4
DIY'er
jamiedolan's Avatar
Rewards Points: 1,024
Will this be feeding 2 bathrooms?
Jamie Dolan - Neenah, WI
Jamie Dolan Paw Dogs
Need Help Uploading Photos? Click here.
jamiedolan is offline   Reply With Quote
Old 05-14-2011, 08:12 PM   #5
Rewards Points: 1,016
Suggest you tag and annotate the wire in the panel so the next guy does not see the larger wire and think a larger breaker is ok.
Old 05-15-2011, 07:06 AM   #6
Electrician
SD515's Avatar
Rewards Points: 504
I might have jumped the gun...is that cable 10/3 with ground? (black, red, white, bare)?
Assuming it is....
As vsheetz suggested, it's a good idea to tag the 10/3 in the panel that it's a 20A circuit. You can use a 20A/2-pole breaker, have one 'hot' feed the powder room and feed the bath with the other, sharing the neutral. Do you know the rules about feeding a bathroom? If you cap off one of the wires in the 10/3, you'd probably have to run another homerun from the panel to feed the bath receptacle(s).
Kyle
jamiedolan (05-15-2011)
Old 05-15-2011, 02:37 PM   #7
a powder room and a bathroom
Old 05-15-2011, 02:52 PM   #8
DIY'er
jamiedolan's Avatar
Are you aware of the codes relating to wiring bathrooms?
Old 05-15-2011, 03:23 PM   #9
i think you have to have a dedicated circuit for a bathroom. but i simply don't have any more slots available at my panel and it had a shared circuit before.
Old 05-15-2011, 03:42 PM   #10
Question
alternatively, i can use the last remaining slot for a dedicated circuit to the bathroom but then i would need to branch out a non-bathroom circuit (mostly used for lighting) to go into the powder room. do you think that would be better?
thanks
Old 05-15-2011, 04:23 PM   #11
DIY'er
jamiedolan's Avatar
thanks
You can put all the outlets from both bathrooms on one 20A circuit. However; other items such as lights and fans need to be put onto some other circuit. Their load is likely low, so you might be able to sneak them on with something else.
Jamie
Old 05-15-2011, 04:51 PM   #12
do you know the reasoning behind that?
thanks
Old 05-15-2011, 04:55 PM   #13
DIY'er
jamiedolan's Avatar
thanks
Not really. But you can either have the outlets only from the 2 baths on one circuit and the lights / fans on a different (any shared circuit) or you can have a dedicated circuit for each bathroom.
It's often hard to know the exact reasoning behind many of the NEC rules.
Old 05-15-2011, 04:58 PM   #14
Electrician
SD515's Avatar
Rewards Points: 504
A circuit for a bathroom can either (1) supply everything in that bath only, as long as nothing fastened in place, other than lighting, exceeds 50% of the circuit rating (10 amps) (like a heater for example), or (2) can supply receptacles in that and other bathrooms, but only bathrooms and only receptacles.
Kyle
The Following 2 Users Say Thank You to SD515 For This Useful Post:
amakarevic (05-15-2011), jamiedolan (05-15-2011)
Old 05-15-2011, 05:06 PM   #15
thanks but that sounds really more like a code excerpt rather than an actual scientific backing thereof
What type wire to use from transfer switch to outdoor outlet brjl Electrical 32 11-20-2013 08:36 AM
Proper Use of Green Wire Nuts HooKooDooKu Electrical 16 06-29-2012 06:41 PM
Fanimation ceiling fan question: no blue wire from ceiling camrn2006 Electrical 8 03-07-2010 12:19 AM
HALP! Master/Remote Dimmer troubles! Confuserated Electrical 9 02-12-2010 03:30 PM
Old house, new light fixture, too many wires Persephonee Electrical 3 01-15-2007 08:58 AM