Using 208v "B" Phase In Open Delta? - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 06-02-2013, 09:46 PM   #16
Rewards Points: 1,536
If you have 240 volts phase to phase (120/240 volt 3 phase system) and you have 120 volts phase to neutral for two of the phases then you will have 208 volts phase to neutral for the third phase.
I would not rule out abnormal phase shifts resulting in high leg to neutral of something other than 208 volts but if this were to occur (perhaps more likely on an open delta system) then some changes to other voltage relationships willl also occur simultaneously.
The Following User Says Thank You to AllanJ For This Useful Post:
mpoulton (06-03-2013)
Old 06-04-2013, 06:15 AM   #17
My electrician basically confirmed what you guys have said plus what I found searching some of the electricians forums on the internet. You basically can't use the "B Phase" or high leg by itself with a single pole breaker.
I do have one last question. Can I use the "B Phase" with any other phase in order to create 240V single phase? So, for instance, if I had a 240V single phase load could I install a breaker between A-B or B-C in order to power it? Or is the B phase ONLY used for 3 phase power and I have to power all of my single phase loads off of A and C?
Biggen is offline   Reply With Quote
Old 06-04-2013, 08:08 AM   #18
Electrical Contractor
jbfan's Avatar
Rewards Points: 536
Yes, you can use the B phase with either A or C and have 240 volts.
Old 06-04-2013, 01:22 PM   #19
Semi-Pro Electro-Geek
Rewards Points: 2,970
Since you have an open delta transformer bank, you should probably only use the B phase with the A phase, not with the C phase (assuming the second transformer is across A and B). Otherwise you may find that the voltage is unstable.
I am a lawyer, but not your lawyer. And who cares anyways? We're here to talk construction. This is DIY advice, not legal advice.
mpoulton is online now   Reply With Quote
easy open window? Startingover Windows and Doors 9 05-26-2013 05:49 PM
Computer Freeware and Open Source Projects user1007 PC Repairs & Upgrades 11 05-07-2013 10:53 PM
Single Pole vs. Double Pole Thermostat dforeid Electrical 14 08-26-2012 08:12 AM
To open up the kitchen or not timbo59 Building & Construction 15 04-30-2010 01:17 PM
New ball valve leaking half open? sz8 Plumbing 5 01-05-2007 10:46 PM