Use A Shared Nuetral Or Not? That Is The Question. - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 05-23-2008, 01:10 PM   #16
I have the electrical inspector telling me that I can either install the GFCI double pole breakers for these MWBC's or I can add an extra neutral wire so that each circuit will have its own and be on a single GFCI breaker. He says the #10 will take care of any voltage drop issue that I may have with the #12.
I don't want to ruffle his feathers but I would rather go with your suggestions!!! He also said it would possibly save me $$$$$$. I would think that an extra 220 feet of #10 wire would be more expensive than a GFCI dp breaker...maybe not.
Your explanation of a MWBC seems to make more sense to me now so that's the way I want to go. Thanks Stubbie.
Cyndi
Student of the great electrical GURU.....Stubbie!
Cyndi is offline   Reply With Quote
Old 05-23-2008, 02:59 PM   #17
Licensed Electrician
jrclen's Avatar
Rewards Points: 514
Cyndi
Not to jump in on Stubbie, but as he is busy:
Your inspector is assuming you are going to use GFCI circuit breakers. He is thinking a double pole for a multi wire circuit or 2 single poles if you add a neutral. He is missing the GFCI receptacle option as Stubbie drew in his diagram. So, with the MWBC you have a choice between a 2 pole GFCI circuit breaker, or the GFCI receptacles. Cost is the consideration there.
John
jrclen is offline   Reply With Quote
Basement Renovation Question KUIPORNG Remodeling 234 08-26-2008 08:19 AM
Nuetral from feeder cable to main panel question? TW Lucas Electrical 14 05-08-2008 11:33 AM
Basement vapor barrier question rob7young Remodeling 2 04-13-2008 09:10 AM
New service Question Onytay Electrical 1 10-24-2007 05:47 AM
One furnace question and one thermostat question lh0628 HVAC 4 10-11-2007 10:17 PM