I'm trying to find out if it is ok to run #4 aluminum use-2 as a feeder for a shed/shop 60amp sub panel. If I understood the nec correctly #4 is only rated at 55 amps at 60degrees,so I would need #3 correct?
Lupus71 is offline   Reply With Quote
Old 02-26-2013, 07:39 PM   #2
Electrical Contractor
kbsparky's Avatar
1) Are you feeding this underground? Type USE wire is for underground installations.
2) Is your total connected load 55 Amps or less? If so, then you can still use a 60 Amp breaker on the #4 wire.
-KB
Old 02-26-2013, 08:33 PM   #3
Rewards Points: 150
Yes it's underground. Im not sure this is what you meant but I won't be using 55 amps at one time. It doesn't seem like the inspector would allow the 60 amp breaker, but that's why I'm on here!
Old 02-26-2013, 08:40 PM   #4
Rewards Points: 150
These are the main tools that will be in there.I'm not %100 on the lighting yet.
The Following User Says Thank You to Lupus71 For This Useful Post:
Stubbie (02-26-2013)
Old 02-26-2013, 10:01 PM   #5
kbsparky's Avatar
How many of these machines will be operating all at once?
You do not have to include non-coincident loads -- only the largest one if the machines will be used one at a time.
Remember when figuring load calculations, you want to use "240 Volts" as your system voltage. Also, watts = Volts x Amps.
-KB
Old 02-27-2013, 07:01 AM   #6
Rewards Points: 150
Looks like it will be 35 amps.
Old 02-27-2013, 05:31 PM   #7
Rewards Points: 150
So the use-2 is ok to feed a 60 amp sub panel from my current panel even though it's rated at 55?
Old 02-27-2013, 06:02 PM   #8
Sparky
Rewards Points: 510
only if the expected load is under 55 amps, because '55 Amps' is not a standard overcurrent protection size.
Techy is offline   Reply With Quote
Old 02-27-2013, 07:03 PM   #9
Rewards Points: 150
Ok thanks! Im trying to get everything right the first time around.
distribution panel amperage rating tom31415926 Electrical 10 08-26-2012 05:09 PM
Sub Panel GND and mixed 240/120 VAC branch curiousB Electrical 12 01-17-2012 11:49 AM
Critique my Sub Panel rjniles Electrical 18 05-18-2011 12:31 AM
Old House Rewire finnimus Electrical 15 05-13-2011 11:39 PM
turn main panel into a sub panel? tikicarver Electrical 2 01-24-2008 08:37 AM