Use 14/3 Two Circuit W/ Gfci Possible? - Electrical - DIY Chatroom Home Improvement Forum
Old 04-12-2012, 11:24 PM   #1
Use 14/3 two circuit w/ gfci possible?
Running new lines in basement Reno. Wondering, since I already have a 15a double breaker, run 14/3 from that two the washroom and use gfci with one circuit and lights with other?
PerfectFinish is offline   Reply With Quote
Old 04-12-2012, 11:28 PM   #2
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
If washroom=bathroom, then no. Bath recepts need to be on a 20A circuit.
But you could put the entire bathroom on one 20A circuit...or put the lights on a 15A circuit and the GFI on a 20A circuit.
But you cannot use 14-3 for the GFI circuit.
Old 04-12-2012, 11:36 PM   #3
joed's Avatar
Rewards Points: 12,874
Post your location. In Canada you will be fine.
Old 04-12-2012, 11:37 PM   #4
k_buz's Avatar
Good point........
Old 04-13-2012, 05:43 AM   #5
Rewards Points: 1,512
(everywhere in the world where "neutral" conductors are used)
A ground fault interrupter can be used with 3 wire cable (multiwire branch circuit) with the foillowing restrictions:
1. Having the GFCI uinit be a GFCI breaker in the panel, or
2. The load terminals of GFCI receptacles connected to the circuit require additional 2 conductor cables byond that point to extend GFCI protection downstream, or
3, Don't use the GFCI load terminals and instead put an additional GFCI receptacle at each desired location along the MWBC.
The neutral attached to the load terminal of a GFCI unit may not be combined with or bonded to the neutral(s) serving other parts of the circuit not associated with the load terminals of that GFCI unit. The subcircuit fed by the hot load terminal of a GFCI unit must be served by and only by a neutral attached to the neutral load terminal of the same GFCI unit.
(If you use a GFCI breaker, then no additional GFCI units are needed in that circuit.)
The Following User Says Thank You to AllanJ For This Useful Post:
gregzoll (04-13-2012)
Old 04-13-2012, 05:49 AM   #6
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,956
Typically. 14/3 is FINE. The only time you can't use it is if you want to use a GFI breaker, which you do not have, or if you want to share the neutral down stream of a GFI LOAD side.
For you though (in the US) you cannot use a 15A circuit for the bathroom receptacle as has been said.
IMO using 14/3 just because you have the breaker is silly. Don't base your wiring plan on the fact that you have a used $8 breaker.
Old 04-13-2012, 05:50 AM   #7
k_buz's Avatar
3, Don't use the GFCI load terminals and put an additional GFCI receptacle at each desired location along the MWBC.
This wouldn't work if the wiring at the outlet box consisted of a 3 wire in and a 3 wire out.
Old 04-13-2012, 05:54 AM   #8
Sure it would.
Old 04-13-2012, 06:04 AM   #9
k_buz's Avatar
I think you are wrong about that. The common neutral would not balance out with the hot supplying the GFI.
Old 04-13-2012, 06:08 AM   #10
As long as you are using only the LINE terminals you can treat it just like a standard receptacle.
The Following User Says Thank You to Speedy Petey For This Useful Post:
jbfan (04-13-2012)
Old 04-13-2012, 06:17 AM   #11
k_buz's Avatar
I see the thanks and will drop out now.
Old 04-13-2012, 11:40 AM   #12
all great advice and help.
just wanted to say thanks to everyone for your advice and help. the owners of this house before i bought it did some incredibly dumb and insane wiring. I had live power behind the walls (both 110,220) just hanging there. I ended up ripping the basement out and now i've decided to run all new electrical to the whole house. felt like mike holmes taking everything down and exposing cheap and brutal work. in my main floor washroom they drywalled over the heat duct (just one of many drywalled over in the house) and made a spaghetti factory of the electrical with a total of 6 junction boxes (all loose in the wall). sometimes i think we should be able to sue or atleast beat the crap out of anyone who does work like this. They install a new panel just to cover up all the electrical crap that was in here. but thanks again for all help. greatly appreciated.
Old 04-13-2012, 03:20 PM   #13
Rewards Points: 242
I just had this done...samething...we pulled two new wires...one 14/2G (15A breaker) for the bathroom lights and vent fan and lights, and a 12/2G (20A breaker) for the GFCI and other outlets for the hair dryers, etc.
Ed911 is offline   Reply With Quote
Old 04-13-2012, 03:22 PM   #14
I would use 12-3 not that much more in cost and better performance
msmith5554 is offline   Reply With Quote
Old 04-13-2012, 07:33 PM   #15
Rewards Points: 242
I used 12/2 with and unsheathed copper ground...why would 12-3 be better...for indoor use? Hot, neutral, and earth ground.
Just inquisitive. I had a licensed electrician do the installation and wiring after I bought all the parts. No likey the shocky...lol...
Oh, I see, you meant to use 12-3 instead of 14-3...right...like I used for my lights.
One of the reasons that I used 14-3 for my lights, is that they, along with my vent fan will never use over 2-3 amps.
Tags
14/3 , gfci
GFCI in middle of circuit packer_rich Electrical 15 11-30-2011 12:38 PM
Stairway light powered from GFCI circuit? jeh179 Electrical 10 03-23-2011 08:57 AM
GFCI Outlet on 20A garage circuit campos202 Electrical 2 09-10-2009 09:38 AM
GFCI Trips campbellpt Electrical 28 11-21-2008 03:06 PM
GFCI circuit Cossack Electrical 31 03-21-2008 12:34 AM