UPS Tripping 20A GFCI In Basement - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 09-18-2010, 12:58 PM   #16
Seasoned DIYer
Rewards Points: 150
You could float the ground pin, then use a mA meter to measure the current going to ground.
IT equipment are FCC listed for both home and office(commercial) use, but that only covers EMF noise considerations. Computer equipment rooms are not GFCI'd and many IT support equipment are not designed to be used downstream of highly sensitive residential GFCI.
HVAC_NW is offline   Reply With Quote
Old 07-27-2013, 02:27 PM   #17
The battle between UPS and FGCI
A UPS does lots of things that a GFI does not like -- as mentioned in posts above: bad power factor, leaky grounds, high inrush.
In the past, we have used "power conditions" to clean up nasty conditions like these. You want a passive "resonant" conditioner that is basically a giant coil (transformer) and capacitor that resonate at 60 Hz. You put this inline and it cleans up voltage/current phase shifts and sudden changes well. It is not a voltage regulator per se, and not a surge protector.
Or, try a different brand of GFCI. They all behave differently.
cow_duo
cow_duo is offline   Reply With Quote
Old 07-27-2013, 03:35 PM   #18
joed's Avatar
Rewards Points: 12,898
This post is 3 years old. I hope the issue is resolved by now.
The Following 3 Users Say Thank You to joed For This Useful Post:
frenchelectrican (07-27-2013), jbfan (07-27-2013), Speedy Petey (07-27-2013)
Tags
ups gfci trip
Cutting out a concrete basement floor jeffhoward001 Building & Construction 21 01-17-2012 08:51 PM
Arcfault GFCI breaker tripping shogy Electrical 4 10-17-2009 02:28 PM
GFCI Trips campbellpt Electrical 28 11-21-2008 03:06 PM
new gfci on new circuit pops rtoni Electrical 39 11-15-2008 10:18 AM
having trouble with the gfci tripping paul110h Electrical 37 06-12-2008 10:30 AM