Upgrading Range Wiring - Electrical - DIY Chatroom Home Improvement Forum
Old 08-22-2009, 05:31 PM   #1
Hello, I have done some searches but haven't quite found the answer I need. I am hoping that the knowledgeable people here could help me out.
I am replacing the electric range in my kitchen. My current wiring has a three-prong outlet, and my understanding is that since this is not new construction (or a mobile home), I would be OK continuing to use a 3-prong outlet.
However, is there any reason that I could not just add a ground line and switch out the 3-prong with a 4-prong outlet? My thinking is that I could run the existing 3-cord wire into a junction box below my kitchen and run a ground wire into the box from another source. Then I could run the 4-cord wire out of the box up into my kitchen into a 4-prong receptacle.
Is there any reason this would not be acceptable (or safe)?
Thanks for any help
-Marcus
PitPat is offline   Reply With Quote
Old 08-22-2009, 10:33 PM   #2
You can't run a ground wire from another source
It does not meet code
Old 08-22-2009, 11:03 PM   #3
2 comments for the price of one...!
My first comment is about the [new] picture on your Blog ID. This doesn't look like Scuba Dave, at all! It rather looks likes ...Newman (what, me worry), of MAD magazine of which I was a big fan!
My second comment is about poster #1. You answered correctly that a ground/(ing) wire can't come from another source than the cable. But, to my knowledge a Three wire NM cable has a bare wire for grounding built into it. So, if the cable supplying the range is a 8/3 or 6/3 there is no problem using a 4 prong plug! Or I misread the original question. (Now more than ever)Don't Drink and Drive!!!
spark plug is offline   Reply With Quote
Old 08-22-2009, 11:24 PM   #4
Electrical Contractor
kbsparky's Avatar
In fact, you are allowed to do this on existing non-grounding circuits.,
Starting with the 1999 NEC, section 250-130 was added to the Code, which states in part:
"(C) Nongrounding Receptacle Replacement ...... The equipment grounding conductor of a grounding-type receptacle .... shall be permitted to be connected to ....
(1) Any accessible point on the grounding electrode system ....
(2) Any accessible point of the grounding electrode conductor
(3) The equipment grounding terminal bar within the enclosure where the branch circuit .... originates ...
-KB
Old 08-22-2009, 11:43 PM   #5
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
As kbsparky said... perfectly fine to do so as long as it is as the code states. You can't connect it to another equipment ground in another branch circuit. It also needs to be sized correctly...a #10 awg copper will do nicely. I almost think that sometimes it would be about as easy to just run a new 4 wire branch circuit to the panel. I wouldn't lose sleep over just leaving 3 wire either.
If you elect to run the ground wire use the correct clamp if your connecting to the metal water pipe within 5 feet of where it enters the house or a grounding electrode or grounding electrode conductor don't use a freakin hose clamp....
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Old 08-22-2009, 11:52 PM   #6
Thank you for the responses.
The existing 8/3 NM wire does not have a bare ground built in, just the white/red/black wires. However, all of the new 8/3 NM I could find did have a bare ground wire built in.
I wasn't planning on tapping into the ground of another circuit, but rather back to the grounding rod itself. But if I would actually need to ground to the bar in the box to met code, than it probably wouldn't be much more work to re-run a 4-cord wire (or just leave the 3-cord and stop trying to make more work for myself).
Thanks again
Old 08-22-2009, 11:55 PM   #7
Woops, I didn't catch the edit before I responded.
So, it would be OK to run straight to the grounding rod? (provided I use the correct clamp ). I'm on a well and I don't know how much I would trust my water lines to provide a decent ground.
Old 08-23-2009, 12:00 AM   #8
UAW SKILLED TRADES
Stubbie's Avatar
Yes it would but make sure the ground rod conductor wire goes to the panel intact and is not broken. Use a ground rod clamp called an acorn clamp...
Stubbie
Old 08-23-2009, 12:05 AM   #9
Will do.
Thanks!
Need help on Electric range wiring rarquilla Electrical 20 11-20-2008 08:00 PM