-   -   Upgrading an Outlet to 20 Amp /120 V grounded GFCI type (http://www.diychatroom.com/f18/upgrading-outlet-20-amp-120-v-grounded-gfci-type-158748/)
Unicornz0 10-02-2012 07:33 PM
I've recently had a home inspection & 1 of the things to be repaired is the bathroom electrical outlet. The report reads Duplex receptacle shall be 120 Amp /120 V grounded GFCI type. I think it should read Duplex receptacles shall be 20 Amp /120 V grounded GFCI type.
I'm wondering how to determine if the in wall wiring will support a 20 amp outlet. How can this be determined? And if it will not, is it reasonable for the Inspector to require this, and about how much will it cost to have a 2nd floor bath wired to accommodate this type of plug. I believe the service is 100 amp service because the 2 main circuit breakers are 100 amp each. Will the current service panel support this type of plug & wiring?
Thanks In Advance,
Uni
jbfan 10-02-2012 07:40 PM
When was the house built?
Where are you located?
The current code requires a 20a, gfci circuit, but does not require a 20 amp receptacle.
allthumbsdiy 10-02-2012 07:43 PM
I can understand the GFCI part, but I can't figure out why someone would mandate a 20 amp circuit in a bathroom, unless you are running some heavy duty heat lamp on that circuit.
20 amp vs 15 amp receptacles are slightly different (one prong on a 20 amp rated circuit has a short horizontal slot).
Best way to see if the wiring is capable is to trace the circuit back to the breaker. If it has a 15 amp circuit breaker, assume that wiring is rated only for 15 amp usage.
Before going crazy with getting quotes, I would ask the inspector to clarify his or her report/
good luck
Unicornz0 10-02-2012 07:47 PM
The house was built in Michigan in 1963.
Thanks.
jbfan 10-02-2012 07:51 PM
Thanks.
Gfci's were not required then, and are not required now.
It is a good idea to replace with a gfci.
Unicornz0 10-02-2012 07:52 PM
good luck
There is nothing heavy duty there. Do you know what the national electrical code requires?
Thanks,
Uni
allthumbsdiy 10-02-2012 07:56 PM
are you buying or selling your house?
i am not an electrician so I would defer to jbfan's statement.
it is my understanding that unless i am changing existing circuits, any electrical wiring would be grandfathered to when it was first installed.
so i would change it to gfci (as jbfan said) for your personal safety but get a clarification from the inspector.
good luck
AllanJ 10-02-2012 07:57 PM
Short answer: Buy the 20 amp GFCI receptacle and install it to replace the old broken receptacle.
Really, you should first take the cover off the outlet box and insert a thin wood stick. If the box is only 2-1/2 inches deep and has more than one cable's worth of wires coming in, it might not be possible to install a GFCI receptacle there and you would need to install a GFCI breaker down in the panel instead. If there is any 14 gauge wire in that circuit or if you are unsure, then the breaker is limited to 15 amps.
Unicornz0 10-02-2012 07:58 PM
I'm planning on buying.
But if I have to rewire the house, I'd likely pass on this one.
Thanks.
allthumbsdiy 10-02-2012 08:01 PM
Originally Posted by AllanJ (Post 1022441)
Short answer: Buy the 20 amp GFCI receptacle and install it.
Really, you should first take the cover off the outlet box and insert a thin wood stick. If the box is only 2-1/2 inches deep and has more than one cable's worth of wires coming in, it might not be possible to install a GFCI receptacle there and you would need to install a GFCI breaker down in the panel. If there is any 14 gauge wire in that circuit then the breaker is limited to 15 amps.
You can have a 20 amp GFCI receptacle (assuming it fits physically) even if the circuit itself is 15 amps.
so i could plug in a device that draws 20 amp on a wire that is rated for 15 amp?
i thought you can install 15 amp receptacle on a 20 amp circuit, not the other way round?
LooseSCruz 10-02-2012 08:03 PM
I can understand the GFCI part, but I can't figure out why someone would mandate a 20 amp circuit in a bathroom, unless you are running some heavy duty heat lamp on that.
My girlfriends ConAir hair dryer pulls just north of 15A all by itself when it's on the highest setting. Just an example.
allthumbsdiy 10-02-2012 08:04 PM
Thanks.
Is this a foreclosed / short sale?
House buying decision is yours to make, but if this is the only "issue" raised, I would not be upset over it.
jbfan 10-02-2012 08:06 PM
Thanks.
As long as the house was built to code, there is nothing that needs to be done.
This issue becomes a point of negotiation between buyer and seller.
I'm sure there were other issues the HI citied that may be more pressing.
AllanJ 10-02-2012 08:09 PM
Fifteen amp receptacles are permitted on a 20 amp circuit provided that the total number of receptacles is at least two singles or one duplex.
Nothing wrong with plugging a device into a 14 gauge wired circuit that could draw 20 amps but if you turn it on high so it actually tries to draw all 20 amps then it will (should) trip the maximum allowed 15 amp breaker.
Unicornz0 10-02-2012 08:09 PM
The Municipality has required this upgrade.
Thanks.