Upgrading 2x100amp Disconnect From H Type Fuses To Cb - Electrical - DIY Chatroom Home Improvement Forum
Old 07-14-2011, 12:29 AM   #1
JVO
Upgrading 2x100amp disconnect from h type fuses to cb
I have an old disconnect with 2x100amp+1 neutral, secured by 2 h-type fuses.The service wires are 2/0.
Can I replaces the h-type fuses by adding a new box with 2x100amp circuit breakers?
If so what type of breakers, what wire size (new box right next to the old disconnect) and what type of conduit?
Can I just run the 2X100amp through the new breaker box or do I have to connect the neutral as well (all the existing wiring remains, only the h-fuses would be replaced)?
Any advice would be appreciated.
JVO
JVO is offline   Reply With Quote
Old 07-14-2011, 11:09 AM   #2
Rewards Points: 78
You need a single phase 100 amp disconnect. Just buy the breaker type. Wires back the same way. There will be a place to connect the neutrals and the grounds. If you connect nuetrals and grounds at this disconnect, they need/must not be connected anywhere else. So check the main panel first.
This will be hot. You will need to have the utility pull the meter. I would suggest you hire someone.
Fused disconnect or unfused, motor is fed from breaker... Do It Right Electrical 17 03-19-2011 01:28 AM
Would upgrading to 200 amp service solve this problem? NancyNGA Electrical 7 03-01-2011 09:38 PM
service entrance cable type & size Chuck S Electrical 5 01-08-2011 11:14 PM
Wiring Size Calculations for New Service CorinthWest Electrical 7 12-07-2010 12:36 PM
Need help with Type T and TL fuses? Fotoguy Electrical 6 03-04-2008 02:08 PM