Upgrading To A 200 Amp Main Service Panel - Electrical - DIY Chatroom Home Improvement Forum
Old 05-28-2009, 05:45 PM   #1
Upgrading to a 200 amp main service panel
I would like to upgrade my service to 200A panel, but i have a few questions.
Do I have to use the cold water pipe to ground the panel ?
Can I use two ground rods 8 feet apart ? or Is concrete encasd electrode safe enough to be the only grounding means, do I need another electrode?
And if anyone can help me with any information regarding the meter up to the weatherhead. i know i have to buy the meter base, but do i get a new meter from the utility company (use the same one, buy new one)
edmart2 is offline   Reply With Quote
Old 05-28-2009, 06:32 PM   #2
300zx's Avatar
Meter
8 Feet apart is good has to be 6 feet or more. Meter where I live the homeowner owns.You can pick up at supply or maybe hd not sure on hd .Not sure about bonding the water line I would do it just to be safe.
300zx is offline   Reply With Quote
Old 05-28-2009, 06:49 PM   #3
dSilanskas's Avatar
Do I have to use the cold water pipe to ground the panel ? YES
EVEN IF YOU USE THE CONTRETE ENCASED ELECTRODE YOU NEED TO USE GROUND RODS ALSO AND 6' MIN is what is required.
YOU REUSE THE METER THAT IS ALREADY THERE. JUST REPLACE THE METER SOCKET ITSELF.
dSilanskas is offline   Reply With Quote
Old 05-28-2009, 06:57 PM   #4
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,956
Meter pan and all other service equipment is purchased and installed by the homeowner or contractor. SOME area POCOs do provide the entrance and meter pan, but not many.
If you have a CCE (concrete encased electrode) NO other supplemental electrode is required to be added. If a metallic water pipe exists and is in contact with the ground for 10' or more then that must also be used as an electrode. The connection to the water pipe must be made within 5' of entering the building.
If the water pipe entering the house is plastic but the household system is metallic then you still have to bond the pipes, but this can be done anywhere at an accessible location.
You/they re-use the meter itself. This is always provided by the POCO.
It is extremely rare that you would be allowed to even touch the meter. DO NOT REMOVE IT yourself! Contact the POC to see what their requirements are.
Typically for a homeowner install they will come and remove it and replace it once you are done and the job is inspected.
Speedy Petey is online now   Reply With Quote
Garage Wiring issues jimmyfloyd Electrical 20 06-08-2009 02:57 PM
Extending Old Main Circuit Panel lkpowell Electrical 4 10-23-2008 02:15 PM
Adding a second Electric sub panel TW Lucas Electrical 9 10-05-2008 02:37 AM
New service panel + Generator transfer Nhrafan Electrical 1 04-21-2008 11:05 PM
2x100a sub on service main jambud Electrical 17 03-12-2008 09:31 AM