Updating Wiring For Detached Garage Question - Electrical - DIY Chatroom Home Improvement Forum
Old 09-21-2011, 10:49 PM   #1
Updating wiring for detached garage question
I just bought an older home and just figured out the garage shares a 15amp circuit with 4 bedrooms and the laundry room.
The house has 125amp service.
My goal: is to get 30amps to the garage and have a 240v receptacle for a future welder, lathe, compressor, etc. And some 120v 15 and 20 amp receptacles and over head lights.
I can easily run a new line from the main to the garage subpanel through the crawl space/attic of the home. The main panel is about 50 feet from the garage plus factor in another 20misc feet.
My plan: Is to purchase a 30amp double pole breaker, (for the main) and then run 8/3 romex.
My question: Is this a good start? I'd like to make sure, that I can run a 240v line then take it back down to 120 with various 15amp and 20amp breakers.
inlet510 is offline   Reply With Quote
Old 09-21-2011, 11:33 PM   #2
Electrical Contractor
kbsparky's Avatar
You'll need a small sub-panel for the garage.
With #8/3 romex, you should be able to use a 40 Amp breaker in your main panel.
From the new sub-panel, run your circuits for the outlets and lighting on separate breakers.
-KB
Old 09-22-2011, 12:49 AM   #3
JOATMON
ddawg16's Avatar
Rewards Points: 1,116
Ditto.......
Just make sure you don't have more than 6 breakers in the sub.....and do not tie the ground and neutral together in that sub panel....
Some juristdictions would also require a ground rod at the garage.
Old 09-23-2011, 12:03 PM   #4
If I ran 30amps, could I run 10/3? Or would that be pushing it? A book I have says to factor in some buffer room, but at the same time the cable should already have that engineered into it right? Theres never going to be a constant 30amp load, it may get up to 27 for a few seconds at a time.
I'm trying to save some money but at the same time be safe.
Also what type of wire do I use for the short overhead run from the house to the garage? UF rated wire?
Old 09-23-2011, 01:31 PM   #5
Licensed electrician
Rewards Points: 1,234
Is the garage attached or detached?
Old 09-23-2011, 01:32 PM   #6
Code05's Avatar
Rewards Points: 1,104
You can use 10/3 UF on a 30 amp breaker if you support it independently with a messenger cable.
Since you going to a residential garage, which is subject to vehicular traffic, a minimum height of 12' is needed for the entire span.
Code05 is offline   Reply With Quote
Old 09-23-2011, 01:36 PM   #7
Code05's Avatar
Title says detached. Who knows?
Old 09-23-2011, 01:40 PM   #8
Code05's Avatar
Unless there is a main breaker or disconnect.
Never heard of one that did not for a sub- panel and two is the norm.
Old 09-23-2011, 01:48 PM   #9
This was the part that raised the question.
Old 09-23-2011, 01:51 PM   #10
Code05's Avatar
Gotcha, I missed that.
Old 09-23-2011, 02:49 PM   #11
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,142
Canada CEC apparently does not require ground rods for a sub panel in an outbuilding. OP does not list his location.
Coastal South Carolina
rjniles is offline   Reply With Quote
Old 09-23-2011, 03:02 PM   #12
To clarify, the garage is detached, I would be running the wire through the home to the back of the home where the original wire drops down from the 2nd story to the garage so clearance isn't a problem.
I do know about the ground rod and will be picking up 2? My question is what type of wire do I use for the transition from the home to the garage.
Attached is a pic, I'm in California you can tell by the sun in my illustration.
Old 09-23-2011, 03:08 PM   #13
JOATMON
ddawg16's Avatar
Correct....forgot to put that in.....ask me how I found out.......
That has been a topic of disccusion over on the garage forum I'm on.....believe it or not, there are some parts of the country who do not require/enforce it....
Some say, if you have a sub in your house, there is no way to install ground rods in addition to what you already have...hence, why would a detached garage need ground rods as long as you run the ground from your main to the sub.....
Of course, there is a big difference between a sub in your house and a detached garage some distance from the house.
Old 09-23-2011, 03:22 PM   #14
Code05's Avatar
You can add as many rods as you like to a house, they just cannot substitute as an EGC.
Questions regarding wiring 220 to attached garage... John Green Electrical 0 01-20-2011 10:23 AM
garage / bedroom wiring code question 205bhamjim Electrical 4 01-20-2010 10:55 AM
Garage Heater Wiring ceiling penetration Question DenverBob Electrical 5 12-28-2009 02:01 PM
Detached Garage Load Question andyjk1 Electrical 14 10-19-2009 03:32 PM
Garage - Protecting wiring installation eastment Electrical 4 11-26-2005 12:52 PM