Underground Wiring To Tool Shed - Electrical - DIY Chatroom Home Improvement Forum
Old 07-30-2012, 04:41 PM   #1
underground wiring to tool shed
Hi,
need some help on this. We plan to place a shed about 70 feet behind our house. The plan is to place pvc conduit underground and then feed 14 /2 Romex through the conduit to power the shed. We expect a light load on this feed, probably one overhead light and one double outlet (110 vac). Outlet will get occasional use for power tool charging. Is this OK to do or do I need a more substantial wiring ?
Dick Dube is offline   Reply With Quote
Old 07-30-2012, 04:45 PM   #2
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Originally Posted by Dick Dube View Post
Hi,
For one, you cant use NM Cable (Romex)
Personally I would just pull out #12 THHN/THWN conductors, 2 hots, a neutral and a ground.
Old 07-30-2012, 04:48 PM   #3
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,274
Nope. Can not run NM underground. Use UF direct buried or 3 runs of THWN in conduit. UF would be easiest. Install a GFCI receptacle at the house and take the UF feed from it. You only need to trench to 12". Use a short piece of PVC conduit to protect it above ground.
Coastal South Carolina
Old 07-30-2012, 04:48 PM   #4
Rewards Points: 14,312
Always better to pull a larger wire then you think you need then to have to go back and redo the whole thing later when you decide to start running tools out there at some point.
Old 07-30-2012, 05:00 PM   #5
A "Handy Husband"
rjniles's Avatar
Come on guys, he is placing a shed behind his house. Most likely a prefab 10 by 12 max. His plan is a light and a power tool charger. Sounds like a single 15 or 20 amp circuit is plenty.
IMHO no sense adding additional $$ for no reason.
Old 07-30-2012, 05:09 PM   #6
E2 Electrician
I know what he 'thinks' he is going to need, I didn't ask him to install a subpanel, but to not take advantage of a multiwire branch circuit is just silly, the money is such a small fraction of having not to repull one conductor at a later date. This isn't my first pony ride, and I've been there done that.
The Following 3 Users Say Thank You to stickboy1375 For This Useful Post:
Calc (08-03-2012), hummer4x4guy (07-31-2012), mpoulton (07-30-2012)
Old 07-30-2012, 05:29 PM   #7
I also have seen it time and time again.
I only need a light and an outlet, what do I do now I bought a table saw at a yard sale and it makes the lights dim or trips the breaker.
Then they have to buy all new wiring.
Last one I worked on they had added 6 outlets 4 more lights, two attic fans, and now wanted to run an A/C unit all on a 14-2 wire.
Old 07-30-2012, 08:14 PM   #8
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
More then one circuit requires a panel suitable for use as service equipment and ground rods and ......,
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
Old 07-30-2012, 08:15 PM   #9
Semi-Pro Electro-Geek
Rewards Points: 2,990
A multiwire branch circuit is considered one circuit.
mpoulton is offline   Reply With Quote
The Following 2 Users Say Thank You to mpoulton For This Useful Post:
andrew79 (07-30-2012), stickboy1375 (07-30-2012)
Old 07-30-2012, 09:36 PM   #10
E2 Electrician
Sorry, but nope. Read 225.30, last sentence.
Old 07-31-2012, 08:27 AM   #11
So others do not have to look it up (from the 2011 edition):
225.30 Number of Supplies. A building or other structure that is served by a branch circuit of feeder on the load side of a service disconnecting means shall be supplied by only one feeder or branch circuit unless permitted in 225.30(A) through (E). For the purpose of this section, a multiwire branch circuit shall be considered a single circuit.
Where a branch circuit or feeder originates in these additional buildings or other structures, only one feeder or branch circuit shall be permitted to supply power back to the original structure, unless permitted in 225.30(A) through (E).
If it were me, I would run 12/3 UF or four 12 gauge THWN - red, black, white, and green.
brgmgb is offline   Reply With Quote
The Following User Says Thank You to brgmgb For This Useful Post:
stickboy1375 (07-31-2012)
Old 07-31-2012, 08:09 PM   #12
Rewards Points: 328
Would DC work?
With a light load I was wondering if you could go with a transformer AC to DC. Then you can run the wire to the shed just a few inches deep like on outdoor lighting.
puttster
puttster is offline   Reply With Quote
Old 07-31-2012, 08:18 PM   #13
electures's Avatar
puttster
Transformers do not convert AC to dc. do you mean low voltage lighting?
Old 08-03-2012, 07:29 PM   #14
Rewards Points: 328
Exactly!
Wiring a shed, need advice. hgbpro Electrical 22 02-02-2012 09:25 AM
Underground Wiring From House to Garage Virginhomeowner Electrical 7 05-21-2010 10:53 PM
Wiring a Shed and Garage abedj Electrical 1 05-08-2009 11:09 AM
Detached shed wiring sketh24 Electrical 3 02-17-2009 04:32 PM
Wiring a shed ocoee Electrical 3 06-05-2007 04:25 AM