Underground Wiring - Electrical - DIY Chatroom Home Improvement Forum
Old 08-30-2011, 12:47 PM   #1
underground wiring
I want to run underground wire (gray wire) to a shed. Want to put a heater 1500W (12.5amp) and a ceiling fan/light and a couple outlets. Will 12 Gage wire with a 20 Amp breaker work. The run is right at 100 feet from breaker box to shed, 60 underground.
btzerr is offline   Reply With Quote
Old 08-30-2011, 12:50 PM   #2
I=E/R
a7ecorsair's Avatar
Nope.....
By gray wire can we assume you mean UF?
a7ecorsair is offline   Reply With Quote
Old 08-30-2011, 01:08 PM   #3
underground wiring
yes UF wire
Old 08-30-2011, 01:18 PM   #4
Code05's Avatar
Rewards Points: 1,104
12/3 UF on a 2 pole breaker would work. GFCI and disconnect needed.
Code05 is offline   Reply With Quote
Old 08-30-2011, 01:29 PM   #5
underground wire
why 12/3 and a 2pole breaker?i am running 110 not 220? i was planning on a GFCI.
Old 08-30-2011, 01:34 PM   #6
Code05's Avatar
2 110v branches of one circuit. No rods needed.
Old 08-30-2011, 02:03 PM   #7
underground wiring
OK i understand the 2 for one run. what do you meen by no rods needed?
Old 08-30-2011, 03:16 PM   #8
Code05's Avatar
A single circuit to a structure does not require that ground rods or such be installed.
250.32 Buildings or Structures Supplied by a Feeder(s)
or Branch Circuit(s).
(A) Grounding Electrode. Building(s) or structure(s) supplied
by feeder(s) or branch circuit(s) shall have a grounding
electrode or grounding electrode system installed in
accordance with Part III of Article 250. The grounding
electrode conductor(s) shall be connected in accordance
with 250.32(B) or (C). Where there is no existing grounding
electrode, the grounding electrode(s) required in 250.50
shall be installed.
Exception: A grounding electrode shall not be required
where only a single branch circuit, including a multiwire
branch circuit, supplies the building or structure and the
branch circuit includes an equipment grounding conductor
for grounding the normally non–current-carrying metal
parts of equipment.
The Following 2 Users Say Thank You to Code05 For This Useful Post:
danielrg (08-30-2011), NJMarine (09-06-2011)
Old 08-31-2011, 02:07 PM   #9
underground wiring
CODE05,
thank you for all your assistance.
Old 09-01-2011, 10:54 AM   #10
Just call me Andrew
Rewards Points: 1,020
Using 3 wires (+ground) with a 2-pole breaker is called a multiwire branch circuit. You have 2 circuits that share a neutral.
Andrew
secutanudu is offline   Reply With Quote
Old 09-06-2011, 04:37 PM   #11
I'd consider running #10. 1500W heater plus outlets has the potential to produce quite a draw. Add 100ft of wire to the equation and I'd want to be safe over sorry.
//Just my 2 cents.
italie is offline   Reply With Quote
Old 09-06-2011, 08:19 PM   #12
Missouri Bound's Avatar
Devils advocate.....if a 3 wire + ground describes a multiwire branch circuit....doesn't it also describe a feeder to a sub panel?
Old 09-06-2011, 10:40 PM   #13
Taking stuff apart is fun
Exactly what I thought when I read it. Why isn't the subpanel just considered a switch / intricate junction box on that same branch circuit then?
butchbs1985 is offline   Reply With Quote
Old 09-06-2011, 10:50 PM   #14
Are you really Brian Maxwell?
Old 09-06-2011, 10:55 PM   #15
Indeed I am but of course not the one and only. Are you really Bound in Missouri?
All wiring underground, yet power outage...? PCMLR Electrical 2 10-10-2010 11:20 PM
underground wiring oldman56 Electrical 6 06-24-2009 07:46 PM
Underground wiring to pump rolltested Electrical 10 04-29-2009 12:15 PM
electric wiring in house remodel wis_remod Electrical 6 04-02-2009 03:40 PM
Knob & Tube wiring - How concerned should we be? hotdiggitydog Electrical 6 04-11-2006 08:52 PM