Underground Run To Outlet For Pool. LB Fitting Out Of Siding? - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 06-25-2012, 07:51 AM   #16
Rewards Points: 242
Originally Posted by Jim Port View Post
That is the idea. Typically the LB would be more flush to the siding.
In the post I found the photo on the person did say the LB was more flush after final install
collegetry is offline   Reply With Quote
Old 06-25-2012, 07:57 AM   #17
Rewards Points: 242
Let me ask another question. Say in place of the LB fitting on the outside of the house, I wanted to have an outlet at that location. Couldnt a box be installed instead of the LB, a GFI in the box, then from load of GFI run wires down out of box thru pvc conduit in the trench to the location of the pool pump outlet?
If I used an LB fitting I would just drill a hole hru siding into rim joist. But with a box, I dont think I could just attach that to vinyl siding.
What type of box could be installed on the siding?
Would a mounting block be needed?
Old 06-25-2012, 08:22 AM   #18
Electrical Contractor
jbfan's Avatar
Rewards Points: 424
When you mount the box on the outside, don't tighten the screws so much that they pull the siding in.
This could require longer screws.
I would not feed the gfci at the pool from the load side of the gfci at the house, but I would use 2 gfci's.
This is just my opinion, as it will work either way.
Old 06-25-2012, 08:32 AM   #19
Licensed electrician
Rewards Points: 1,506
You might be able to use one of these boxes.
http://www.aifittings.com/catalog/si...aded-openings/
Old 06-25-2012, 09:43 AM   #20
Rewards Points: 242
Thanks alot. Looks like the FS8141T for 1/2" double 4 siding is what i need.
Old 06-25-2012, 10:41 AM   #21
Rewards Points: 812
OP is running conduit the entire trench. Does that mean you cannot run UF (say 14-2 UF) cable inside the conduit then? That you have to run THWN wires inside the conduit? Seams it would be easier to just pull UF cable through but I don't think NEC allows this. Does someone know for sure and possibly a code reference?
curiousB is offline   Reply With Quote
Old 06-25-2012, 11:19 AM   #22
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Since this is a pool, he cannot use UF, he has to use THWN, with a minimum #12 awg insulated equipment ground.
Old 06-25-2012, 11:24 AM   #23
Rewards Points: 242
Thanks for this info. I was planning on using the individual wires but did not know it was required since a pool was involved.
Old 06-25-2012, 11:26 AM   #24
E2 Electrician
If the is a permanently installed pool, you will have to keep the GFCI 10 feet from the pool, or not less than 5 feet with a single receptacle, twist lock and GFCI protected.
You will also need a general purpose receptacle 10' min, 20' maximum from the pools edge.
Old 06-25-2012, 11:29 AM   #25
E2 Electrician
This only applies to a permanently installed pool.
Old 06-25-2012, 04:38 PM   #26
Rewards Points: 2,516
680.22A1Receptacles that provide power for motors/pumps/loads that directly relate to the circulation and sanitation system shall be located at least 10ft from the inside walls of the pool or not less than 6ft from the inside walls of the pool IF they meet ALL of the following:
-single receptacle
-locking configuration employed
-grounding type
-have GFCI protection
680.22A3 A permananently installed pool must have at least one 125V 15 or 20 A receptacle on a gen-purpose branch circuit that is located a minimum of 6ft, but no more than 20ft, from the pool's inside wall. This receptacle must not be more than 6.5ft above the floor, platform or grade level serving the pool.
hammerlane is offline   Reply With Quote
Old 06-25-2012, 04:43 PM   #27
E2 Electrician
-single receptacle
-grounding type
The part in bold is only for the 2011 NEC, and yes, it is 6', not 5' as I stated.
Old 06-25-2012, 05:34 PM   #28
Rewards Points: 242
-single receptacle
-grounding type
thanks for all the info but what in the world does a single locking grounding type GFI look like?
Old 06-25-2012, 05:38 PM   #29
You won't find one. The pump probably comes with a regular prong plug. This is one of those areas where I wish the code and the manufacturers come come to agreement.
Old 06-25-2012, 06:35 PM   #30
E2 Electrician
Jim, I've never seen a pump come with a cord unless it was a storable pool. And I've wired a lot of pools.
New siding up to existing soffit jtchavez Building & Construction 18 03-25-2012 09:48 AM
Outlet before light switch; Open Neutral? Fox Electrical 21 09-26-2010 08:38 PM
European 220V outlet "Schuko" estophile Electrical 6 08-27-2005 08:45 AM
Siding: Cement Vs. Cedar Grumpy Remodeling 5 03-19-2005 01:07 PM
Siding: Aluminum vs. Vinyl Grumpy Remodeling 1 03-19-2005 12:55 PM