Underground Run To A Garage - Electrical - DIY Chatroom Home Improvement Forum
Old 05-05-2011, 05:30 PM   #1
Rewards Points: 2,240
Underground run to a garage
Need some advice.
We're doing some excavating around our building and we're going to uncover
an underground connection to the detached garage.
Had problems with the wiring in the garage (that will be dealt with) -
the line going into the garage is "Romex", 12 - 2, no bare copper wire.
Don't know yet, if the buried wire is "UF".
We'll find out what it is tomorrow.
Question is - we're going to replace it -
run PVC, Sch. 40 - then Romex (12 -3) - or can we pull 12 - 3 wires inside
the PVC?
Any thoughts?
Thanks!
rossfingal
rossfingal is offline   Reply With Quote
Old 05-05-2011, 06:02 PM   #2
Licensed electrician
Rewards Points: 1,892
If you are going to run conduit you would install individual THWN conductors in the proper sizes and colors.
Type NM-B cable cannot be used outside, even if in conduit.
rossfingal (05-05-2011)
Old 05-05-2011, 06:19 PM   #3
Jim Port
Would PVC be considered adequate (as conduit) - or metal?
Already know about grades of wire.
Thanks!
rossfingal
Old 05-05-2011, 10:14 PM   #4
Mad Scientist
Check with your local inspectors to be sure, but by the NEC you may use Sch 40 PVC conduit underground; it must be buried deep enough to have 18" of cover over it. Where the pipe is exposed to physical damage (where it comes out of the ground to enter the side of the structure) you must use Sch 80 PVC.
McSteve is offline   Reply With Quote
The Following User Says Thank You to McSteve For This Useful Post:
Old 05-05-2011, 10:18 PM   #5
I ask the impossible!
Rewards Points: 712
Some locals might say otherwise but where I am the way my AHJ reads NEC the riser is subject to physical damage. So that means that my choices for conduit for the riser are schedule 80 PVC or intermediate metal conduit or rigid metal conduit.
Schedule 40 PVC would be allowed for the run. There are tables for the depth at which it has to be buried, and somebody will correct me if I remember wrong. I think you have to bury schedule 40 18", you can direct bury UF cable at 24" and rigid metal conduit you can bury as little as 6".
Please do NOT consider any "before" picture of my house as any kind of endorsement of any particular construction method. In fact, you should probably assume that if I post a "before" picture, I am posting it because I am soliciting advice on a proper replacement for one of MANY things done wrong by a previous owner.
WillK is offline   Reply With Quote
The Following User Says Thank You to WillK For This Useful Post:
Old 05-05-2011, 10:25 PM   #6
Missouri Bound's Avatar
Are you planning to use the garage as a workshop? If so consider putting a panel in the garage for expansion purposes. Then you could put in larger conduit and perhaps install a 60 to 100 amp service in the garage. You will need a few more things, such as a panel and grounding rod with proper attachment, but it will give you flexibility in the future. Schedule 80 will be fine, and the depth will be determined by it's location....that is it would be buried deeper if under a driveway.
The Following User Says Thank You to Missouri Bound For This Useful Post:
Old 05-05-2011, 10:27 PM   #7
Mad Scientist
Good point. I would say that if you're only going to run a 20A MWBC, run large enough conduit that you can upgrade to at least a 60A feeder later without digging it all up again.
Old 05-06-2011, 04:52 AM   #8
Thanks all, for the advice!
At least I have something to show the boss!
I'll find out today what the old wire is.
Probably going to use 1 1/2 inch PVC, with suitably rated 12-3 Romex -
1 1/2 inch conduit out of the ground.
(Digging sure is fun! - ha, ha!)
Thanks again!
rossfingal
Old 05-06-2011, 05:39 AM   #9
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,276
rossfingal
NIX on the Romex, not rated for wet locations like the conduit.
Coastal South Carolina
The Following User Says Thank You to rjniles For This Useful Post:
rossfingal (05-06-2011)
Old 05-06-2011, 10:32 AM   #10
rjniles
Yeah, just talked to a friend of mine (licensed elect. Cook County,Ill. - that's
where we're at) - moisture/water problems.
Probably, go for direct bury - 2 ft. down.
Thanks for the "heads up" advice!
(Don't think it's going to be shop/home-shop)
rossfingal
Old 05-06-2011, 10:39 AM   #11
Mad Scientist
I'm not sure what you mean by "moisture/water problems" but in my opinion, THWN wire in PVC conduit, or even UF cable in PVC conduit, is a far superior installation to UF cable direct-buried in the ground, for future upgradability and reliability. UF cable in the ground will eventually fail. Without conduit, any repair or upgrade down the road is going to require trenching again.
Personally, I will use UF cable to feed a lightpost or post-mounted outlet, but always conduit between buildings.
That's just my advice though, you can take or leave it. Direct burying UF cable for this installation is also perfectly legal.
Old 05-06-2011, 12:35 PM   #12
McSteve
I'm here to get some guidance.
As far as I'm concerned, I don't think 1 1/2 PVC, as an underground run,
would not be unacceptable - at least, it can be upgradeable.
What we have is 12-2 Romex, not even a bare-copper ground.
No markings - no stamps - nothing.
(I haven't seen that too much!)
It's 30 - 40 - 50, years old (Don't know).
If we're going to replace it: I just want it to be - somewhat, "up to snuff".
Thanks for the input!
Regards!
rossfingal
Do I have a Fire Rating Issues with Attached Garage Perry401 Building & Construction 4 04-25-2011 11:58 PM
Underground antenna cable from detached garage PaulTurner Electrical 4 04-07-2011 07:08 PM
Underground Wiring From House to Garage Virginhomeowner Electrical 7 05-21-2010 10:53 PM
Garage Wiring issues jimmyfloyd Electrical 20 06-08-2009 02:57 PM
