Underground Electrical Service - Electrical - DIY Chatroom Home Improvement Forum
Old 06-27-2010, 04:44 PM   #1
Underground electrical service
I am in the process of running an underground electrical service from my house to my workshop. I plan on running 220v 75A service using #3 Awg copper direct buried cable. The distance between my house and the workshop is 150' but Im not sure if I need to use conduit.
armyeng is offline   Reply With Quote
Old 06-27-2010, 05:08 PM   #2
I would use conduit with individual thwn wire. Dig it once and you can always change the wire down the road if need be. Don't forget you need 4 wires H H N G and keep the neutrals and grounds seperate in the panel in the workshop and you need ground rods.
Plumbvoltage is offline   Reply With Quote
Old 06-27-2010, 06:35 PM   #3
#3 direct burial is good for 85a
#3 individual THWN is good for 100a
Conduit is the better choice
Old 06-27-2010, 08:11 PM   #4
nap
You talking to me?
nap's Avatar
Rewards Points: 6,290
Huh?
Not all direct burial cable is rated the same. UF is rated for 85 amps but I don't know if you can even get #3 UF. Most people would use USE which is rated for 100 amps (#3 cu).