Under Cabinet Lighting Wire Size - Electrical - DIY Chatroom Home Improvement Forum
Old 09-29-2012, 04:12 PM   #1
under cabinet lighting wire size
I have a switch that was wired for an outlet under the sink maybe for a disposal which I don't have instead I used the switch to power four 12" flouresant T-5 under cabinet lights. I direct wired the lights together one to the other then but I ran out of 12/2 wire and instead ran 9' of 14/2 wire to the last light, it was late Sunday night and I wanted to get done. From the switch to the first light is in the wall the rest of the wire is exposed, inside the cabinet's. This is all that I can find on the 20 amp circuit.
I've since read here that 20 amp breakers normally use 12/2 wire.
Do I need to go back and change the 14/2 to 12/2 for the last light?
I ask because:
  1. it's a pain in the but to fit all those wires in those small lights
  2. they came with lamp cord that could have been used to jump from one to the other
  3. they're on a switch that is off 90% of the time.
Thanks in advance
gcan is offline   Reply With Quote
Old 09-29-2012, 04:20 PM   #2
Licensed electrician
Rewards Points: 1,026
You cannot protect a #14 with a 20 amp breaker. You can either replace the #14 or change the breaker to 15 amps.
Old 09-29-2012, 04:24 PM   #3
Rewards Points: 1,192
Read about tap rules. You are legal.
bobelectric is offline   Reply With Quote
Old 09-29-2012, 04:54 PM   #4
bob - I'll read the tap rules - thank you
Jim - protect it? surely the 14/2 can handle more than the lamp cord that comes with these lights
I do not know how to change a breaker, actually being a DIY'er I have always avoided working in the main panel
Old 09-30-2012, 08:13 AM   #5
what gauge is standard lamp cord? With the code requiring certain gauge wire for safety are the cords also regulated?
My point being on my garage I used the lamp cord provided to plug in the undercabinet lights and then daisy chained two other lights again with the wire provided.
Should I change those lighs as well?
Old 09-30-2012, 08:48 AM   #6
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
If those lights came as a kit and the instructions say you are able to do it that way, they also probably give you a limit of how many lights you can wire together using the lamp cord. If you stay within those manufacturer specs, you are fine.
Old 09-30-2012, 08:52 AM   #7
The load on the fixture wires is known. This is why they are allowed to be smaller. The load on building wiring is not known and needs to be sized properly in order to be protected by the breakers.
Old 09-30-2012, 09:09 AM   #8
(just trying to understand) - how is it different using the supplied cord between two lights and using 14/2 instead of 12/2 between two lights? my original post has 12/2 from the switch to all but the last light which I jumped to with 14/2, all tied together and the wire is exposed, but now it has ti be changed?
Old 09-30-2012, 09:15 AM   #9
k_buz's Avatar
Because the lamp cord supplied with the undercabinet lights were approved by UL for certain specifications/uses. Those are stated in the instructions. There are probably special connectors that have to be used that came prefabbed on the cords as well. When you extend the circuit with your own 14-2 romex, you are giving the impression that this wiring is part of the house wiring and someone in the future can connect more lights/receptacles off this circuit. If more lights are connected, that lamp cord which may be as small as 16-2 now could have 20A of current running thru it causing a fire hazzard.
Old 09-30-2012, 09:17 AM   #10
It may seem to be an issue of semantics, but the electric code is not written to allow the last portion of the circuit to be smaller like in your example.
Old 09-30-2012, 09:19 AM   #11
Could you please expand on how this would be legal?
The Following 2 Users Say Thank You to Jim Port For This Useful Post:
k_buz (09-30-2012), stickboy1375 (09-30-2012)
Old 09-30-2012, 09:19 AM   #12
k_buz's Avatar
Also, consider if someone did connect to that last fixture to install say a shop light, that shop light will not be grounded. Your typical lamp cord does not carry a ground.
Old 09-30-2012, 02:26 PM   #13
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Incorrect...
Old 09-30-2012, 06:26 PM   #14
" Euro " electrician
frenchelectrican's Avatar
Vous êtes sérieux ?
( You are serious ? )
Merci,
Marc
under and in cabinet lighting fabian General DIY Discussions 2 10-10-2011 11:04 PM
wire size question analogmusicman Electrical 8 09-01-2011 07:17 PM
ceiling fan wicked97 Electrical 4 08-21-2011 09:12 AM
Size of Wire & type of wire agman Electrical 6 11-10-2009 09:13 PM
wire size wire to 10kw furnace? lochcarron Electrical 1 04-10-2005 08:43 PM