Old 05-01-2011, 08:14 AM   #1
UF in PVC pipe
I guess I should of asked first.
I needed to run about 25' of conductors through a sill into some PVC pipe to wire a GFCI receptacle, a flood light device and a switch in water tight boxes. I planned on running THWN in the conduit but I could not find any locally by the foot (500' rolls were my only choice). So someone suggested using UF cable which I did and it ran just fine.
I just noticed two things. UF uses THHN conductors? I assumed it was "W", and is rated for 60 degrees? My light wanted 75 degrees.
Thank you
whatrymes is offline   Reply With Quote
Old 05-01-2011, 08:24 AM   #2
Just call me Andrew
UF in PVC pipe
How big was the conduit? Was it gray electrical conduit, or white PVC pipe?
Andrew
secutanudu is offline   Reply With Quote
Old 05-01-2011, 08:57 AM   #3
UF in PVC pipe
It is gray 1/2" electrical conduit, oh, and for clarity, it runs up a wall, there is nothing underground.
Old 05-01-2011, 09:10 AM   #4
Electrician
SD515's Avatar
UF in PVC pipe
Where did you get the 60* rating? NEC Table 310.16?
Check the package, if it's UF-B cable it probably has THHN/THWN, rated 90 degrees C. Also, UF (Undergroud Feeder) cable is going to have conductors rated for wet locations.
It's been a long time since I used UF cable, so I'm trying to pull out an old memory bank...
Kyle
Old 05-01-2011, 09:14 AM   #5
Lic Elect/Inspector/CPO
UF in PVC pipe
This uf can be used in pvc pipe.
NJMarine is offline   Reply With Quote
Old 05-01-2011, 10:06 AM   #6
UF in PVC pipe
You're fine.
bobelectric is offline   Reply With Quote
Old 05-01-2011, 10:18 AM   #7
Unhappy
UF in PVC pipe
I got the info from a web site selling cable, that's why I wanted to ask. It is UF-B.I have an old code book, 1999 time to upgrade
Old 05-01-2011, 10:25 AM   #8
UF in PVC pipe
This is from the manufacturer "Southwire":
Multiple conductor UF-B cable may be used for interior branch circuit wiring in residential or agricultural buildings at conductor temperatures not to exceed 90°C (with ampacity limited to that for 60°C conductors) as specified by the National Electrical Code.
I didn't notice that before.
Old 05-01-2011, 11:29 AM   #9
nap
You talking to me?
nap's Avatar
UF in PVC pipe
I try to never believe, at least without verifying, that the manufacturer states regarding code compliance. Since the code is updated every 3 years, things change. If you have material older than 3 years, their statement may no longer be correct. Beyond that, I have seen manufacturers claim code compliance when it actually wasn't or it was compliant in a very limited use that was not applicable to most installations.
additionally, their statements are often confusing for the layman. Your example is one that can confuse a lot of people unfamiliar with the intent.
as you pondered before, an updated code book is the best source of information. It is the only truly dependable source of information because, well, those are the rules you have to follow. If it doesn't meet the requirements in the code, it doesn't matter what the manufacturer says about it.
Old 05-01-2011, 11:31 AM   #10
Electrical Contractor
UF in PVC pipe
The conductors are rated for 90 degrees, but the code limits the ocpd to the 60 degree column, so you are fine.
Yes I am a Pirate, 200 years too late. "Jimmy Buffett"
Old 05-01-2011, 03:07 PM   #11
UF in PVC pipe
I think I understand,
Thanks again
Best way to join Poly pipe, for a water pipe repair. carl1864 Plumbing 9 08-21-2011 03:17 PM
Well pipe access shutdown HomerRepair Plumbing 6 03-08-2011 10:22 AM
Qs about the 1/2"dia brass pipe we bought smoochas Plumbing 10 02-21-2011 10:23 AM
What’s the best way to remove pipe from T Jaylyn Plumbing 2 02-03-2011 02:05 AM
First Furnace Install - Need Some Help Getting Started hartkem HVAC 17 10-11-2008 12:55 PM