MrAngles 10-11-2012 10:22 AM
I'm finishing my basement, and decided to add a subpanel for power down there. I'd like to use a 50 or 60 amp breaker in the main panel, but I'm not clear on what wire to use to run to the subpanel. I can't seem to find any romex in 6 gauge or bigger at the big big stores, but I did find this online: http://www.wesbellwireandcable.com/R...mexnmb6-2.html Should I be using romex, or should I be using individual wires in a conduit? Will I need higher than 6 gauge to support 60 amps?
J. V. 10-11-2012 11:36 AM
The wire in the link can be purchased from a local electrical supply house. But, you need 6/3 NM. Not 6/2 NM. You must run four wires to the sub. H-H-N-G.
MrAngles 10-11-2012 12:23 PM
Thank you, what's the additional wire for?
kbc 10-11-2012 12:56 PM
the additional wire is for the ground, in a main panel nuetrals and grounds can be together but in a sub panel they hav to be isolated
MrAngles 10-11-2012 02:29 PM
Isn't 6/2 three wires, hot, neutral and ground? 6/3 is four leads, right?
BrandonD 10-11-2012 02:33 PM
Correct... 6/3 with ground contains two hots, a neutral, and a ground. One hot would be connected to each pole of your 2-pole feeder breaker in the main panel to run 240V and then connect to the buses in your subpanel (lugs or breaker).
MrAngles 10-11-2012 07:07 PM
Gotcha, cool, thank you.
sublime2 10-11-2012 08:02 PM
Generally speaking the first # in wire description refers to the gauge (thickness) of the wire.
The second # refers to the amount of wires within the sheathing. The ground is almost never referenced in that # but is almost always there.
k_buz 10-11-2012 08:06 PM
You are correct on the gauge, but the second number refers to then number of insulated conductors.
sublime2 10-11-2012 08:20 PM
Tomato, tomAto.
Terminology.
No?
MrAngles 12-29-2012 07:22 PM
Okay I have my 50A breaker, my sub panel and my 6-3 NM wire, with three 6-gauge conductors and a ground.
My sub panel has three lugs, two for hot and one for negative? Where do I hook up the ground? Do I just screw it in anywhere on the negative bar? Also since this is just going from the attached garage to the basement (it doesn't go outside anywhere), do I take the green screw out?
http://imageshack.us/a/img689/9201/subpanel.jpg
(sorry for the poor picture)
http://img543.imageshack.us/i/20121229154254.jpg
rrolleston 12-29-2012 07:46 PM
You will have to add a ground bar.
rrolleston 12-29-2012 07:47 PM
Originally Posted by sublime2 (Post 1029129)
Tomato, tomAto.
Terminology.
No?
Yes it is.
MrAngles 12-29-2012 08:39 PM
Ok I see where the ground bar will pop in on the left side. Do I need to actually ground it to something in the basement, or is it just a spot for the ground wires to all connect to the 6-3 supply wire's ground?
And how about that green screw?
brric 12-29-2012 08:49 PM
Remove the green screw.