Two Romex Wires In 3/4" Conduit - Electrical - DIY Chatroom Home Improvement Forum
Old 05-23-2010, 12:38 PM   #1
Rewards Points: 274
two romex wires in 3/4" conduit
I am running to a two gang box on a temp. power pole (less than a foot length of counduit) and can't use two pieces of conduit due to space, the romex is 12/2 w/ ground...Is this ok?? Or should I just use thhn wire.......(I have to buy the thhn, but already have the romex)
ugabulldog is offline   Reply With Quote
Old 05-23-2010, 08:19 PM   #2
Totally screwed together
Strip off the outer jacket on the romex, don't put that inside the conduit.
If the run is under 24" in conduit, you don't need to worry about derating. You should be OK.
The difference between THHN and romex is that romex conductors wont say they are OK to 90 degrees. But for a short run on a temp setup, you should be fine.
xxPaulCPxx is offline   Reply With Quote
Old 05-23-2010, 08:20 PM   #3
You can't strip the jacket off romex, code violation
You can't use NM romex underground at all or in wet location
Outside would be considered a wet location
Old 05-23-2010, 08:52 PM   #4
Rewards Points: 274
Romex rated for outside is ok, right?
Old 05-23-2010, 08:59 PM   #5
Licensed electrician
Rewards Points: 1,502
NM cable which is commonly called Romex is not for use outside. Type UF is a non-metallic cable that can be used outside.
Old 05-24-2010, 01:07 AM   #6
He's not running the cable outside, he's running it between two boxes, inside conduit. He doesn't need outside rated cable inside the boxes.
While I agree it is a violation to use stripped romex in conduit, the only reason for that is because the cable isn't labeled like THHN is. It would take a super-nitpicky inspector to bounce him on the temporary pole because his brand new wire doesn't have a temp rating on it.
Old 05-24-2010, 01:52 AM   #7
" Euro " electrician
frenchelectrican's Avatar
PaulCP.,
The quickest way the inspector will fail if the OP did strip off the NM and use in the conduit and the NM conductors itself is not printed or stamped like THHN/TWHN if that was stamped then yeah it is not issue but no word or marking on it then no.
For myself I will be becarefull when you denfine " tempory " power set up per NEC code the Tempory power is legit for 90 days however there are few situation it will be more than 90 days then go with permament set up { this one of few area the inspectors may get nitpicky on it and POCO final call as well }
My Inspector is very sharp person and he allready nailed few customer with that with unmarked conductors in the tempory power location.
Merci,Marc
Old 05-24-2010, 04:23 AM   #8
Paul, the NEC defines a conduit outside as a wet location. This would prohibit the NM outside, whether in conduit or not.
Old 05-24-2010, 09:06 AM   #9
I've yet to see a Temp power pole Inside ??
And a code violation is a code violation, none of the NM wire I have seen is marked on the wire, only the casing
On a Temp power pole I'd almost think the Inspector would look it over more carefully
There have been people killed due to an improper installation
And once an Inspector finds you trying to avoid doing something so simple the right way he/she is going to look over all the work more carefully
Old 05-24-2010, 09:25 AM   #10
Rewards Points: 274
The romex is UF (is this not reffered to as romex?), i should of stated this earlier....so I am assuming this is ok??? (yes, I know what they say about assuming)
Old 05-24-2010, 09:32 AM   #11
UF is OK for outside use
But do not strip the sheathing off
Old 05-24-2010, 10:28 AM   #12
Master Electrician
Rewards Points: 3,824
Originally Posted by frenchelectrican View Post
PaulCP.,
Merci,Marc
90 days? You sure must deal with some fast construction companies. Around here we have temps for sometimes over a year.
brric is online now   Reply With Quote
Old 05-24-2010, 01:40 PM   #13
To All: I stand corrected: On conduit being outside as well as stripping romex for a short run inside a conduit riser.
Wire passing through a J-box in a Conduit run theatretch85 Electrical 4 05-22-2010 03:56 AM
Wiring a Spa and THHN question. skleinsmith Electrical 29 04-02-2010 11:41 AM
Connecting Romex at Panel Bocolo Electrical 14 02-21-2009 05:55 AM
Conduit size for four #8 wires goboomers Electrical 1 11-14-2008 09:00 PM
Cost Difference Between Conduit & Romex Shawns4 Electrical 39 08-25-2008 05:01 PM