Rose.... I just spent the last two hours studying all your posts, and from yoyur linguistic style, your composition and subject orientation.... I'm willing to bet (nominal sum) that I can guess the day you were born ..say within 6 1/2 years.
Peter
MTN REMODEL LLC is offline   Reply With Quote
Old 05-21-2013, 02:04 PM   #62
Electrical Contractor
Philly Master's Avatar
Rewards Points: 516
Originally Posted by Jim Port View Post
Article 210.70 only says that lighting outlets need to be installed in certain rooms of which a switched receptacle would satisfy. Other rooms(kitchens and bathrooms) the switched receptacle is not acceptable and the lighting outlet is required.
Agreed
BTW, there is no requirement for a fixture to be installed at the lighting outlet.
The location of the switch is silent except for a few select locations like the attic, basements, and some stair landings.
Agreed.. And there is a requirement for the location of the switch....
Someone could install all the other switches in one room and still satisfy the NEC.
I will paraphrase the Charlie B rule for you. Sometimes the NEC does not say what you think it says.
So what are the exceptions that,I pointed out mean ????
Philadelphia Master Electrician-Generac Dealer
Philly Master is offline   Reply With Quote
Old 05-21-2013, 02:59 PM   #63
Rewards Points: 214
Were you one of those guessers at Six Flags that guessed birthdate, age or weight? OK shoot.
rosem637 is offline   Reply With Quote
Old 05-21-2013, 03:06 PM   #64
Licensed electrician
Rewards Points: 1,266
You quoted them on page 3 of this thread.
(c) Where one or more lighting outlet(s) are installed for interior stairways, there shall be a wall switch at each floor level, and landing level that includes an entryway, to control the lighting outlet(s) where the stairway between floor levels has six risers or more.
(3) Storage or Equipment Spaces. For attics, underfloor spaces, utility rooms, and basements, at least one lighting outlet containing a switch or controlled by a wall switch shall be installed where these spaces are used for storage or contain equipment requiring servicing. At least one point of control shall be at the usual point of entry to these spaces. The lighting outlet shall be provided at or near the equipment requiring servicing.
The location of the switch only applies to what I have highlighted in your quote in blue, nowhere else.
Old 05-21-2013, 04:27 PM   #65
Monday (actually I'm very accurate within 3 Days) All about assumptions we make ...and toggle switches on the wall.
Best Regards
Peter
Old 05-21-2013, 04:51 PM   #66
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Did you read the headings in the section that you posted? You cant take words after one sub-heading and apply them to another sub heading.... in which you were trying to do, you wanted it to say what you thought was code, so you kept reading it the way you wanted to hear it.
The Following 2 Users Say Thank You to stickboy1375 For This Useful Post:
Jim Port (05-21-2013), MTN REMODEL LLC (05-21-2013)
Old 05-21-2013, 04:59 PM   #67
E2 Electrician
Your words ....
And simply not true ....210.70(A)(3). At the very least
210.70(A)(3) only applies to Storage or Equipment Spaces, that's why it has its own heading.
And if you really read 210.70(A)(1) both exceptions #1 and # 2 why are there exceptions ??
Did you actually read that section of the NEC? I don't even know why you are questioning this?
Exceptions to what .....hee heee hee the wall switch
No, the required lighting outlet
I go back to 90(C) ........."or an instruction manual for untrained persons"
That would be you. and i'm not trying to insult you, I just want you to really understand what you are reading.
The Following User Says Thank You to stickboy1375 For This Useful Post:
Old 05-22-2013, 07:44 AM   #68
Rewards Points: 516
Yes ...
210.70(A)(1)
Habitable rooms..at least one WALL SWITCH controlled ...IN every habitual room
Exception # 1 basically gets you out of installing a light ....In lue of a switched outlet but it is still a,switch in the room
Exception # 2 ... (1) and (2) both talk about customary location and in addition to WALL switch
Ok all the same code section...all exceptions to 210.70(A)(1)......all about habitable rooms...
2008 code
Old 05-22-2013, 07:57 AM   #69
Rewards Points: 516
(1) Habitable Rooms.
At least one wall switch-controlled lighting outlet shall be installed in every habitable room and bathroom.
Exception No. 1: In other than kitchens and bathrooms, one or more receptacles controlled by a wall switch shall be permitted in lieu of lighting outlets.
Exception No. 2: Lighting outlets shall be permitted to be controlled by occupancy sensors that are (1) in addition to wall switches or (2) located at a customary wall switch location and equipped with a manual override that will allow the sensor to function as a wall switch.
Old 05-22-2013, 07:59 AM   #70
Yes ...
210.70(A)(1)
Habitable rooms..at least one WALL SWITCH controlled lighting outlet...IN every habitual room
2008 code
You can't leave out words that change the entire context of the article. Again, the code is only saying the lighting outlet needs to be installed in habitable rooms. The switch can be anywhere. Like it or not it does not say what you think it does.
sirsparksalot (05-22-2013)
Old 05-22-2013, 08:12 AM   #71
Rewards Points: 516
There is the whole code ....ONE section only ....Exception (2) (1)
"In addition too".
Or exception (2)(2) ...customary location.....
Old 05-22-2013, 08:15 AM   #72
Rewards Points: 516
Lol now your leaving words it says....one wall switch controlled lighting outlet
Old 05-22-2013, 08:18 AM   #73
E2 Electrician
Yes ...
210.70(A)(1)
2008 code
Lol, that's not what it is saying, read the entire sentence.
Old 05-22-2013, 08:23 AM   #74
Rewards Points: 516
[B]At least one wall switch-controlled lighting outlet shall be installed in every habitable room and bathroom.
I,did ...
Old 05-22-2013, 08:25 AM   #75
E2 Electrician
I,did ...
Read it again, it doesn't say a light switch is required. Just a wall controlled switched outlet.
Why are switches placed furthest from light? cypherx Electrical 17 06-21-2012 06:48 PM
Replacing multi-use light switches jimclark Electrical 4 08-30-2011 03:05 PM
3-way switches, lights, and a photoelectric switch. Your thoughts? Fox Electrical 7 11-23-2010 11:08 AM
2 switches 2 lights line in through light 1 bldaz Electrical 9 12-24-2009 07:42 PM
3 switches 1 light. need 2 lights 2 switches. Im desprete s richards Electrical 6 07-19-2008 04:18 PM