Two Circuits Sharing A Neutral - Electrical - DIY Chatroom Home Improvement Forum
Old 09-10-2011, 04:04 PM   #1
Two Circuits Sharing a Neutral
I recently bought a home in Brooklyn, NY, and in the process of changing out a receptacle, I noticed that I had two 20 amp circuits sharing the same neutral.
It's my understanding that this is fine as long as the 2 circuits are on different phases. What I don't know is whether my circuits are on different phases. They are circuits #12 and #16, meaning that they are in the same column in the panel, with one breaker (#14) in between.
If this means they are on the same phase, am I OK leaving it as is? The circuits get a very light load. If I switched the 20 amp breakers to 15 amp, would that help minimize any risk of overloading the neutral?
Thanks in advance.
brookny is offline   Reply With Quote
Old 09-10-2011, 04:14 PM   #2
Code05's Avatar
Rewards Points: 1,104
most residential panels are odd and even. Move breaker to to 13 or 17, install a handle tie or use a two pole breaker, group circuits in panel with tape or a ty wrap.
Code05 is offline   Reply With Quote
Old 09-10-2011, 04:27 PM   #3
Electrician
SD515's Avatar
Rewards Points: 504
What brand is the panel? Most likely it’s as Code05 said, but if it’s a Push-o-matic one of the breakers will have to go to the left side, and will require a 2-pole breaker to be compliant with code.
Kyle
Old 09-10-2011, 05:15 PM   #4
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,034
Measure voltage across the 2 breakers, if it measures 240 they are on opposite legs of the service. If it measures 0 they are on the same leg.
Coastal South Carolina
Old 09-10-2011, 05:21 PM   #5
Rewards Points: 150
Shouldn't they be on 12 and 14.
Sunny B. is offline   Reply With Quote
Old 09-10-2011, 05:23 PM   #6
Master Electrician
Rewards Points: 3,698
Probably, yes.
brric is online now   Reply With Quote
Old 09-10-2011, 05:27 PM   #7
Rewards Points: 150
Originally Posted by brric
Probably, yes.
So in other words, sometimes that's not the case?
Old 09-10-2011, 06:09 PM   #8
A "Handy Husband"
rjniles's Avatar
Depends on the panel, the most common arrangement is
Left side Right side
A B
B A
A B
B A
etc etc
Format is not working for me, the first column is the left side, second column is the right side.
But some panels are all A leg down the left side and all B leg down the right side.
Old 09-10-2011, 06:39 PM   #9
Rewards Points: 150
A B
B A
A B
B A
etc etc
Wow!! So how would you put a 2 pole breaker on that?
Old 09-10-2011, 06:48 PM   #10
A "Handy Husband"
rjniles's Avatar
The breaker bridges across the left and right side.
Here is an old Zinsco panel with a 2 pole breaker
Old 09-10-2011, 06:54 PM   #11
Rewards Points: 150
Wow. Thanks for enlightening me
Old 09-10-2011, 07:13 PM   #12
Licensed electrician
Rewards Points: 1,052
A more typical arrangement is A A
B B
A A
B B.
This allows a 2 pole breaker to grab the opposite legs.
A common numbering scheme has the odds on the left and the evens on the right, for example 1 2
3 4
5 6 etc
Old 09-10-2011, 07:27 PM   #13
Rewards Points: 150
B B
A A
B B.
3 4
5 6 etc
This is what I'm familiar with. The other panel is what had me lost.
Old 09-10-2011, 07:34 PM   #14
Electrician
SD515's Avatar
Rewards Points: 504
Slight modification for your picture RJ.
Kyle
Old 09-10-2011, 07:43 PM   #15
Code05's Avatar
Originally Posted by brric View Post
Probably, yes.
Okay, I had a brain fart, it happens.
Yes I meant any 2 slots directly above or below each other.
10 and 12, 12 and 14, 14 and 16, 16 and 18, etc.
Unless it is one of those Pushmatics mentioned.
Tags
circuits , neutral wire , phases
installing new dedicated circuit - neutral bus full 7green Electrical 12 05-03-2011 02:32 PM
Bond subpanel Neutral directly to SE neutral using split bolt? Sierevello Electrical 1 01-30-2011 09:08 PM
Induction Cooktop, no neutral (?!) andersol Electrical 7 09-28-2010 04:47 PM
Linking the 5amp lighting live to the 13amp neutral causes tripping of the rcb. Why? StevieV Electrical 8 08-24-2008 10:42 PM
12v diff between ground and neutral at panel am9518 Electrical 7 02-25-2008 07:28 PM